Search the forum,

Discuss to TT or not to TT in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
28
Morning everyone
It seem I have another outside job.
this time the run is 44 metres with about 2 metres going into a chase in a concrete path so calculated for underground.
the job is to supply a double socket at the end of the garden but eventually this will be where a large shed is going to go into which they will want sockets lights and a heater
Board has one spare way but dual RCD
So thinking of putting in a 63 amp fused main switch
then of course an RCD weather proof double socket.

But I've allowed for 38 amps i.e garage unit
so as a section is underground its coming up at 10mm rather then 6mm if all over ground.
by the way i'm using 3 core SWA
That's not the problem.
I just know you like lots of info.

The question is would you TT or not?
and why would you TT or not TT?
I like watching John Ward and he's not a fan of TT so if you would TT would you test it as a ZE an the sub board or test it using the 3 pins

Thanks again for your help
 
The main argument for going TT is when you have a TN-C-S supply and have some issue with bonding extraneous conductive parts. If you are using 3-core 10mm SWA then your CPC size is adequate for bonding on all system.

So really the only remaining issue would be if there was a reason to worry about the bonded metalwork presenting a hazard to true Earth if you were unlucky enough to have a PME fault?
[automerge]1590319120[/automerge]
Final thought: make sure there is enough of the SWA feed to the socket left that it can be used to the final garage CU location. You could do a resin joint later if needed but life is much easier and more reliable if you don't have to!
 
The main argument for going TT is when you have a TN-C-S supply and have some issue with bonding extraneous conductive parts. If you are using 3-core 10mm SWA then your CPC size is adequate for bonding on all system.

So really the only remaining issue would be if there was a reason to worry about the bonded metalwork presenting a hazard to true Earth if you were unlucky enough to have a PME fault?
very true but in that case the whole house would be affected not just the shed, so no to TT in your view?
 
The main argument for going TT is when you have a TN-C-S supply and have some issue with bonding extraneous conductive parts. If you are using 3-core 10mm SWA then your CPC size is adequate for bonding on all system.

So really the only remaining issue would be if there was a reason to worry about the bonded metalwork presenting a hazard to true Earth if you were unlucky enough to have a PME fault?
[automerge]1590319120[/automerge]
Final thought: make sure there is enough of the SWA feed to the socket left that it can be used to the final garage CU location. You could do a resin joint later if needed but life is much easier and more reliable if you don't have to!
Thanks but have allowed for and extra 6 metres which will be coiled up as they don't know exactly where the shed is going
 
very true but in that case the whole house would be affected not just the shed, so no to TT in your view?
Generally if you have a reliable TN-derived earth then you should use it.

The issue is when you have something conductive outdoors that is on the CPC and if it were to go to ~100V under the rare PME fault condition it would be a hazard. Just now the focus has been on EV chargers for this case (with someoene washing the car when a fault occurred, etc), but in the past it was prohibited for building sites, etc.

Typical outdoor power tools like lawnmower, hedge-trimmer, etc, are not an issue as they are mostly double-insulated.
 

Reply to to TT or not to TT in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top