TT system, Zs on socket circuit is 77.2 down a good bit after I added a second earth rod.

When I short neutral to earth RCD doesn't trip.

Can anyone help me out and explain please.
 
If there’s no current flowing in the circuit the RCD won’t see the fault.
And I would not recommend doing it this was as there is a risk of shock.
 
With TT and sometimes TN a connection between neutral and earth may not create an imbalance whereby the circuit may decide to still use the path of least resistance, neutral.
 
With TT and sometimes TN a connection between neutral and earth may not create an imbalance whereby the circuit may decide to still use the path of least resistance, neutral.
That's what I thought, I'm not used to TT installations, they're not the norm where I am.
I'm just used to it popping straight away with TNCS.

Maybe a few more rods might lower it enough to trip.

Thanks
 
At the point you have shorted N and E, you have 2 paths back to the transformer, in parallel:

The neutral conductor, say approx 1 ohm, and
The earthing system, about 77 ohms.

To trip the 30mA RCD, gonna need >15mA straying to earth.

V = IR
V = 0.015 X 77
V between short and trans = 1.155V

I = V/R
I = 1.155 / 1
I in neutral conductor = 1.155A

So an absolute theoretical minimum of 1.170A flowing in the neutral at the short to trip the RCD (probably need a lot more in practice).


The current straying to earth might not come from that circuit, it might come from others on the same RCD. In which case the same calculation, but now the 2 paths would be:

Neutral conductor from N bar back to transformer, say about 0.1 ohm, and
N conductor of socket circuit from N bar to the short, then back to transformer via earthing system, about 78 ohms.

0.015 X 78 = 1.17
1.17 / 0.1 = 11.7A flowing in the N bar
 

Reply to TT system, earth to neutral not tripping RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
588
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock