Search the forum,

Discuss Tumble dryer extension plug melted. in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
12
Six years ago, I had a double socket installed in my store room. This was placed next to the fuse box and its purpose was so I could connect my tumble dryer.

The socket was too far away from the dryer, so I bought some 1.5mm flex and wired in an extension from the newly installed double socket, to where my dryer was installed. Length of the flex would be 2 metres. The flex is tacked along the wall and connected to a 1 gang socket (screwed onto the wall) which has the tumble dryer plugged in.

Everything worked fine until today.

I was using the dryer and noticed the plug on my extension was extremely hot. Opening the plug, I noticed it was burning near to the fuse. It was all brown.

The dryer plug, which is plugged into the extension, was not hot and that plug is okay (although it is molded so cannot see inside).

I have checked the 1.5mm flex, and the 1 gang socket which I connected to the flex, and there does not seem to be any damage.

I have put a new plug on the extension and left the dryer running, with me being there, in case the new plug got hot and started to melt.

All the way through the dryer in use, which was around 30 mins, the plug did get warm (which I would expect from something using nearly 3 kW) but nothing which I would say was a concern.

The circuit, which this plug socket was installed, has a RCD, but it did not trip.

So, I am trying to work out why the original plug melted? Suggestions would be appreciated.

Thanks.
 
It was probably a poorly manufactured plug top and changing it should sort it out. I personally would have used 2.5mm flex for the extension lead as tumble driers are hungry beasts.
 
If you have the plug, post a picture of it please :)

If it melted around the pin itself, then it's likely down to a bad connection between the plug and the socket, would most likely be accompanied by browning of the socket around the pin. If it's melted the plug top (may also melt the pin), it could be a loose connection around the area of the melting. So, if the area around the fuse terminal that connects to the live has melted, it could be a loose fuse clip, which wouldn't be that uncommon, especially if it's been in use for a long time, the normal thermal cycling can cause the spring clip to loose tension.
 
DSC_1070.JPG
 
The fault is the fuse clip was loose.

If the flex shows no signs of heat damage, putting a new plug on it (buy a good quality one) should see it back in use with no ill effects.

A 3 core flex clipped direct should be able to handle 17.5A. It will get warm, but not excessively so. So, as @Rpa07 has said a better choice would have been a heavy duty extension using 2.5mm flex.
 
I appreciate the time you have spent and am glad, in the grand scale of things, it was nothing serious - although glad I caught it.

I will replace the extension with the higher grade cable.
and fit a decent quality plug. the 1.5mm cable is fine though. you dryer takes around 10A (when heating). 1.5mm is good for 18A. it's the plug/socket connections that cause problems.
 

Reply to Tumble dryer extension plug melted. in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Prima Tumble Dryer which I have had for 5 years. Just recently, the plug and socket melted. I replaced both and it melted again. I...
Replies
18
Views
3K
My tumble dryer broke, an electrician put a new and stronger capacitor in, couple months later I realised that the socket on the extension lead...
Replies
7
Views
3K
Hi am just looking for some expert advice, my little girls room only has 1 double socket, currently have an extension lead with just the camera...
Replies
5
Views
219
I have just bought a tumble dryer that has come supplied with A 13A fuse. The manual says it has come with a special plug, that must be plugged...
Replies
14
Views
3K
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock