Trying to get this thread back on topic:- You can not have have 2 circuits from the same OCPD. You can have one radial socket circuit with a spur from the MCB if feeding only one point!

Discuss?
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.
 
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.

Branching off a radial is fine from a socket. Branching from a MCB?...... I was thinking along the lines of separation of circuits but at the end of the day, if it was a RFC in the first place it would serve the same floor/area so no difference really.
 
no, you can have unlimited branches. it's only that you can have 1 unfused outlet from a RFC, tapped off at theOCPD.

But remove the RFC leaving the 2.5mm radial with one double outlet on the 32A MCB and it suddenly becomes dangerous and against the regs, much in the same way that an insulated consumer unit will inevitably catch on fire now it's not to regulations.
 

Reply to two radials on 16 a mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top