What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 .

The lights are.67 and the is a socket radial circuit which is at .51 .
 
Welcome. You need to build up the picture a bit at a time, starting with the Ze.
Remember Zs = Ze + (R1+R2)
....so if Ze is ok then the answer lies with the circuit itself somehow.
(The two other circuits you mention suggest the Ze is within limits.)

You say it's a ring final circuit. Did you do dead end to end tests and figure of 8 tests before the live Zs test?
 
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 .

The lights are .67 and the is a socket radial circuit which is at .51 .
If other circuits are giving under an ohm then it looks like a typical TN system, then having a very high Zs for your RFC really suggests the CPCs are badly connected.

Quite an achievement really, given they ought to form a ring so two connections in parallel...but as @Julie has asked, have you checked the end-end values r1, r2, and rN to see if it looks sane from that point of view?

Another thing is to use a wander lead and see what your resistance from any socket's CPC (e.g. using socket test adaptor) is to the MET, that ought to be consistent with the r2 value and if not its another part of the puzzle that could point the way to an answer..
 
@Lesley19 you are allowed to ask questions, however silly they may seem, if the replies aren’t making sense to you. We all had to start somewhere!
Or did you have an EICR done and this was one of the findings?

@Lesley19 you are allowed to ask questions, however silly they may seem, if the replies aren’t making sense to you. We all had to start somewhere!
Or did you have an EICR done and this was one of the findings?
Hi, it turned out to be a very corroded socket outlet, and not a ring. It was two radials. An EICR had been carried out.
 

Reply to Very high Zs on ring main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock