Hi there
I preface this query with: I am an almost complete electrical novice. I need to control the speed, startup and slow down of a 2100W induction AC motor through a VFD. My workshop has ordinary Australian 240v single phase supply. I can find plenty of VFDs that convert single phase to 3 phase but I can't find a single to single phase unit.Can this even be done? What other options are available?

 
Usually VFD drive three-phase motors as it is hard to get a single phase motor to run well over a wide range.

In reality most "single phase" motors normally uses a capacitor to generate a 2nd shifted phase to get going, and that shift is frequency dependent so not great outside of a moderate range around the designed speed.

Depending on the equipment and your needed speed range it might be worth seeing what it would cost to get a 3-phase replacement motor for it. Typically motors have fairly standard frames (i.e. shaft and fixing means) so it is frequently an easy and reasonably priced job.
 
As PC1966 says the performance of single-phase motors under VFD control is definitely inferior, making single-phase output VFDs something of a necessary evil. They do exist, but if you plan to use one, beware the need to derate the motor quite heavily and the limited speed range over which it will still provide adequate torque.
 
What's the application for?

If it's a lathe, for example, then three phase VFD is better as it offers good torque at low speeds where a single phase motor won't. Poor torque equals a lot of chatter and poor finishing.
 
Thank you for the thoughtful replies. The applications are a 2x72" grinder and a powered hacksaw (home built). I mainly wanted to cushion the start a little (especially for the hacksaw) but I can see now that a 3 phase motor would have perhaps been a better choice. We live and learn!
 
Re#5; You mention you mainly wanted to cushion the start of the machines. You could use one of these:

RS PRO Single Phase Soft Starter - 12 A Current Rating, 2.2 kW Power Rating, 230 V ac Spply Voltage | RS Components - https://uk.rs-online.com/web/p/soft-starts/2096340/

wired between the motor's terminals and the 240V supply/starter. It has a rating of 2.2kW and you stated your motor is 2.1kW. One per motor or you could share it between motors by suitable switching or plug-socket if you only use one machine at a time.
 
Re#5; You mention you mainly wanted to cushion the start of the machines. You could use one of these:

RS PRO Single Phase Soft Starter - 12 A Current Rating, 2.2 kW Power Rating, 230 V ac Spply Voltage | RS Components - https://uk.rs-online.com/web/p/soft-starts/2096340/

wired between the motor's terminals and the 240V supply/starter. It has a rating of 2.2kW and you stated your motor is 2.1kW. One per motor or you could share it between motors by suitable switching or plug-socket if you only use one machine at a time.
Thanks Marconi! That is the answer!
 

Reply to VFD Single Phase in and out in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
829
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
I have a box powering three 3-phase motors off of one 240V single phase line, NEMA 10-30. In the picture you can see a wiring diagram. The...
Replies
8
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top