Discuss Voltage drop calc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
can anyone tell me if this is a correct way of thinking

i have 6 Cleaners outlets off a !6a rcd, total run length is 55m

6mm feed to first point is 30m would give me voltage drop of .78% (using half the breaker load according to exception 1 on page 163 of as 3000:2018)

then run a 2.5mm for the remaining 25m giving me a voltage drop of 1.56% (same exception)

total voltage drop of 2.34% ( i need to be under 3 for this installation)

my main question being is it acceptable to break gauge considering the breaker protects the 2.5mm cable as i cant seem to find it in the rule book
 
in assume you mean a 16A MCB with RCD protection or RCBO. fine as long as the breaker is sized according to the smallest cable on the circuit.
 

Reply to Voltage drop calc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
hello. i need to run power to a cabin that is 350 feet from the service pole in our driveway. the problem is voltage drop. the service pole is 150...
Replies
8
Views
1K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
First, I really appreciate any feedback you can provide. Its awesome to have a group of people that have a passion for this! Our RV Park has a...
Replies
20
Views
6K
Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
Replies
29
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock