Currently reading:
Voltage drop under load

Discuss Voltage drop under load in the Need help with ElectriciansForums.net? area at ElectriciansForums.net

Reaction score
1
Hi, has anyone encountered a similar fault...

TN-C-S supply with old wylex fusebox. Last night, customer experienced total power loss whilst in the shower (electric), nothing tripped and no fuses blown. Customer pulled out fuses to check them and then replaced them all but could only get some lights & TV to work.

I tested voltage on supply side of main switch (220v) in the 'OFF' position and (210v) in the 'ON' position, but then as soon as anything is plugged in, or a light is turned on, voltage instantly becomes unstable, bouncing around between 115v - 180v. Disconnecting the shower made no difference.

I did an insulation resistance test across all circuits and readings are around 48-50MΏ on L-N, L-E & N-E.

I've not seen this kind of fault before. Has anyone else? any suggestions for further investigation would be really appreciated.

Thanks
 
Sounds like a bad connection on the supply side, if the service head is getting hot under load it could be in there. If it's an overhead supply, it could be a bad connection along that route.
 

Reply to Voltage drop under load in the Need help with ElectriciansForums.net? area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock