Currently reading:
Where to buy nylon screws?

Discuss Where to buy nylon screws? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Reaction score
5,659
I want to replace some metal socket screws with nylon screws.

I can only find 25mm ones. I really need a selection, at least 35mm i would think, preferably a few 40mm ones as well.

If they are impossible to find, then I guess I could use the extenders, but I'd much rather have a selection of varying sized nylon.

Does anyone know where to purchase them?
 
There's plenty on the internet.....but interested to know why you need them for socket outlets, they're part of the earthing arrangement.
Generally used for light switches where no earth is available.
 
There's plenty on the internet.....but interested to know why you need them for socket outlets, they're part of the earthing arrangement.
Generally used for light switches where no earth is available.
And perhaps arguable then too.

410.3.9 - Provision for fault protection may be omitted for the following equipment:
...
(iii) exposed-conductive-parts which, owing to their reduced dimensions (approximate maximum of 50mmx50mm) or their disposition cannot be gripped or come into significant contact with a part of the human body and provided that connection with a protective conductor could only be made with difficulty or would be unreliable
NOTE: This exemption applies, for example, to bolts, rivets, nameplates, cable clips, screw and other fixings...
...
(Excuse typos...)

Sparky Ninja has a video on this (from about 6.00) which persuaded me.

Did buy some on ebay a while back anyway, but the only places I've recently come across lighting with no earth the back boxes have been the same vintage, metal with insulated socket tabs so didn't see the need.
 
Only use is electronics.
Non-conducting locations perhaps too? Never seen one in the flesh so don't know the requirements.

I have seen a few properties with rusted back boxes because of damp walls, so I guess plastic back boxes and plastic screws might have a place then.... though probably fixing the damp is the correct long term answer!
 
There's plenty on the internet.....but interested to know why you need them for socket outlets, they're part of the earthing arrangement.
Generally used for light switches where no earth is available.
My mistake. I've always called them socket screws. They are for lights switches.
And perhaps arguable then too.

410.3.9 - Provision for fault protection may be omitted for the following equipment:
...
(iii) exposed-conductive-parts which, owing to their reduced dimensions (approximate maximum of 50mmx50mm) or their disposition cannot be gripped or come into significant contact with a part of the human body and provided that connection with a protective conductor could only be made with difficulty or would be unreliable
NOTE: This exemption applies, for example, to bolts, rivets, nameplates, cable clips, screw and other fixings...
...
(Excuse typos...)

Sparky Ninja has a video on this (from about 6.00) which persuaded me.

Did buy some on ebay a while back anyway, but the only places I've recently come across lighting with no earth the back boxes have been the same vintage, metal with insulated socket tabs so didn't see the need.
Gosh, I didn't know that reg existed! It makes it pretty clear fault protection can be omitted.
 
Slightly off topic, but follows on with the same theme...

I've seen a few youtubers talk about resolving EICR issues where no earth is available at lighting points, and Class I fittings or metal switch plates are installed, by changing to plastic switches and class II lights.

Am I correct in understanding that this is not a suitable solution as they are undertaking work that doesn't meet current regulations?

Might have presented this with poor wording, but hopefully the underlying question is apparent.
 
Slightly off topic, but follows on with the same theme...

I've seen a few youtubers talk about resolving EICR issues where no earth is available at lighting points, and Class I fittings or metal switch plates are installed, by changing to plastic switches and class II lights.

Am I correct in understanding that this is not a suitable solution as they are undertaking work that doesn't meet current regulations?

Might have presented this with poor wording, but hopefully the underlying question is apparent.
BPG4 (EICRs) points us to BPG1 (CU Changes) on this issue.


1621118318781.png

and there's more afterwards for if the customer won't do it.
 
That's clear enough. It was the idea of effecting a solution that wasn't to current regs, which didn't sit right with me.

I should probably read the Best Practice Guides as they may address other issues that I haven't yet reconciled.
 
That's clear enough. It was the idea of effecting a solution that wasn't to current regs, which didn't sit right with me.

I should probably read the Best Practice Guides as they may address other issues that I haven't yet reconciled.
I guess the argument it is that replacing an existing faceplate that causes danger with one that removes that danger is within the spirit of good practice - and that a replacement is not the same as a new installation?

I think in a domestic rental EICR I'd be cautious about doing much in the way of remedial work on a circuit to get a satisfactory in that situation though. But then again the chances of being able to rewire in 28 days are slim, so it is a temporary solution to a present situation.

There are surprisingly many houses that still have that age wiring - a testimony to how well PVC cabling lasts I guess..

I can think of at least 4 properties (only one rental) I've been to in just the last 6 months that were wired that way.
 
My mistake. I've always called them socket screws. They are for lights switches.

Gosh, I didn't know that reg existed! It makes it pretty clear fault protection can be omitted.
Yep, I only ran into it because of the Spark Ninja video, which was mostly about earthing back boxes with a flylead or not - (and he said he would anyway in new installs).

Sometimes I pick up nuggets like this that I'd never get from any amount of time reading the book cover to cover ...
 
It is clear enough in BS7671 that Class II protection should only be used in monitored environments that would not include a dwelling.

Brings us back to my original thoughts, but what about BPG4 statement?

I'm guessing the replacement of Class 1 lighting and metal switchplates, where no CPC is present, would not be acceptable as an initial recommendation, but is it an acceptable means of risk reduction where a homeowner refuses the option of bringing CPC to each point?



I think it was a couple of Nick Bundy videos where he mentioned replacing replacing lights or accessories when CPC had been absent. Perhaps he had discussed options with the client and they had refused all offered solutions, but the way he had commented gave the impression that this was something he deemed to be acceptable.
 
Brings us back to my original thoughts, but what about BPG4 statement?

I'm guessing the replacement of Class 1 lighting and metal switchplates, where no CPC is present, would not be acceptable as an initial recommendation, but is it an acceptable means of risk reduction where a homeowner refuses the option of bringing CPC to each point?



I think it was a couple of Nick Bundy videos where he mentioned replacing replacing lights or accessories when CPC had been absent. Perhaps he had discussed options with the client and they had refused all offered solutions, but the way he had commented gave the impression that this was something he deemed to be acceptable.
It may well be a risk reduction but the wants of the homeowner shouldn't be a factor. If we find this we only give one option and they can take it or leave it, risk reduction wouldn't even be considered it is their home and shouldn't be your problem. As for BPG4 do you follow this or BS7671 Regulation 412.1.2, I know which I will follow.
 
It may well be a risk reduction but the wants of the homeowner shouldn't be a factor. If we find this we only give one option and they can take it or leave it, risk reduction wouldn't even be considered it is their home and shouldn't be your problem. As for BPG4 do you follow this or BS7671 Regulation 412.1.2, I know which I will follow.
I disagree with some points, IMO you have to consider the risks. We all know the correct solution, however if a client refuses then the next best thing needs to happen, removing all class1 accessories and providing class2 to the point of nylon screws (as the thread suggests)
 
I disagree with some points, IMO you have to consider the risks. We all know the correct solution, however if a client refuses then the next best thing needs to happen, removing all class1 accessories and providing class2 to the point of nylon screws (as the thread suggests)
If they refuse they refuse it wouldn't be my problem. This is often found on an EICR so the situation is documented if they don't want the solution we suggest then that is up to them. Fitting Class II fittings may well reduce the risk but how long for, until someone changes it because the situation isn't being monitored.
 
If there were some fatal accident and some smart Barrister pulls up BPG4 , the Judge could turn round and say you have not done enough to minimize the risk , despite BS7671 Regulation 412.1.2 or even any documented EICR (so it becomes very much your problem)

That of cause is only my fear I could be talking rubbish just putting it out there.
 
If there were some fatal accident and some smart Barrister pulls up BPG4 , the Judge could turn round and say you have not done enough to minimize the risk , despite BS7671 Regulation 412.1.2 or even any documented EICR (so it becomes very much your problem)

That of cause is only my fear I could be talking rubbish just putting it out there.
I've carried out an EICR and the situation is suitably documented and if necessary explained to the client, I have done my job the contract is finished. Remedial works/suggestions will be a separate issue and it is entirely up to the client whether they take up these works even if some decide to minimise the risk, it cannot be forced onto the client. BPG4 would not be a factor here my works are following BS7671.
 
I can see both sides of this argument. While it's possible that BPG4 could be used as the basis of a case in these circumstances, it is equally possible that a similar case could be taken against someone who followed the advice in BPG4 as it didn't comply with BS7671.

Not sure why electricians often seem to be placed in the position of having to try finding a means of ensuring the safety of customers who refuse to consider their own family's safety - or that of their tenant.
 
I can see both sides of this argument. While it's possible that BPG4 could be used as the basis of a case in these circumstances, it is equally possible that a similar case could be taken against someone who followed the advice in BPG4 as it didn't comply with BS7671.

Not sure why electricians often seem to be placed in the position of having to try finding a means of ensuring the safety of customers who refuse to consider their own family's safety - or that of their tenant.
I think maybe we will see guidance change a little in the future to distinguish between rental properties where the landlord is responsible for safety, and a private home where the home owner is the one taking the risks.

Or maybe BS7671 should finally get round to making things a lot clearer on how to safely maintain existing installations - and remove some of the doubt.
 
Not sure why electricians often seem to be placed in the position of having to try finding a means of ensuring the safety of customers who refuse to consider their own family's safety - or that of their tenant.
I often think if electricity was wet, runny and messy like water or smelly like gas our lives would be easier.
 
Class11 fittings are recommended as a minimum in above situation and is acceptable. Just record it and jog on. Nylon screws are not required but doesn't mean some wont use them. Think.due to less than 50mm in size or something.
 
I know where ya comming from, but the iet can't reference bpg and then others questions to believe its ----. Your a very precise electrician westward or maybe engineer... but you know if they cant afford new wires, best thing todo is remove metal fittings. Where there to help not dictate.
 
Just to throw a spanner in the works....... the current BPG4 has nothing to say on this (issue 5)
 

Reply to Where to buy nylon screws? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock