DIY
Reaction score
10
Hi to all. Is there legal requirement for additional dedicated RCD even if we have Double RCD CU?
Our whirlpool bath has ambiguous instructions: first it saying that it has to have separate RCD outside. Then it says "IF separate RCD installed" like if there as an option not installing it.
We have double RCD CU and it has spare switches in case if dedicated wire is needed.
 
It absolutely must have RCD protection. Given the very high risk of water and electrics together then having a 2nd RCD in series just for the tub is not a bad thing as it reduces the chance of a single failure leaving it unprotected.

Also should there be some fault with the tub that trips them, you will be able to reset the house one without having to determine the tub is at fault and separately isolate it.

Is this a small one that plugs in to a 13A socket or something the needs a dedicated feed? For 13A outlets you can get outdoor rated RCD sockets that might be a simple solution if outdoors, or indoor versions.

EDIT: Also check the specifications, normally domestic RCDs are 30mA rated but you might find the manufacturer recommends 10mA in which case it will need a special choice (you can get 13A RCD sockets with 10mA trip as well).
 
It absolutely must have RCD protection. Given the very high risk of water and electrics together then having a 2nd RCD in series just for the tub is not a bad thing as it reduces the chance of a single failure leaving it unprotected.

Also should there be some fault with the tub that trips them, you will be able to reset the house one without having to determine the tub is at fault and separately isolate it.

Is this a small one that plugs in to a 13A socket or something the needs a dedicated feed? For 13A outlets you can get outdoor rated RCD sockets that might be a simple solution if outdoors, or indoor versions.

EDIT: Also check the specifications, normally domestic RCDs are 30mA rated but you might find the manufacturer recommends 10mA in which case it will need a special choice (you can get 13A RCD sockets with 10mA trip as well).
It says 30ma and there was a milliseconds specs as well, I even bought 2 of those rcd spurs as soon as I read the manual. It just the other day I noticed that on the other electrician formum they mostly against additional rcds on already protected by rcd circuit. Even argued that it may fail building control etc , others argued that even if it not necessary as long as it is not harmful it is okay) That’s what made me doubt. Looks like the regulations are fairly ambiguous)
 
It will not fail building control, where did you see that? You'll need appropriate test gear to ensure the rcd is operating correctly too. If there circuit is already protected by the appropriate rcd then there is no need to add another. The circuit will also need tested and certified to ensure it meets regulations.
 
yet here people posting that whirlpool bath tub will benefit from extra rcd on already cu-rcd protected circuit. so what is going on? or is it extra safety just for peace of mind beyond reasonable requirements?
 
It will not fail building control, where did you see that? You'll need appropriate test gear to ensure the rcd is operating correctly too. If there circuit is already protected by the appropriate rcd then there is no need to add another. The circuit will also need tested and certified to ensure it meets regulations.
yet here people posting that whirlpool bath tub will benefit from extra rcd on already cu-rcd protected circuit. so what is going on? or is it extra safety just for peace of mind beyond reasonable requirements?
 
Looks like the regulations are fairly ambiguous)

The regulations aren't ambiguous on the matter, they require 30mA RCD protection to be installed for various reasons.
In the average domestic installation this means that RCD protection is required for all final circuits at the CU.

Everything else you have read online, here and elsewhere, is people's opinions on what can be done over and above the regulations.

The wiring regulations set a minimum standard, most of us try to exceed that standard.
 
The regulations aren't ambiguous on the matter, they require 30mA RCD protection to be installed for various reasons.
In the average domestic installation this means that RCD protection is required for all final circuits at the CU.

Everything else you have read online, here and elsewhere, is people's opinions on what can be done over and above the regulations.

The wiring regulations set a minimum standard, most of us try to exceed that standard.
if some electricians confident that extra rcd is required despite being already on cu-rcd circuit and some including you (perhaps) -- not , then this is the evidence of ambiguity (IMHO)
 
if some electricians confident that extra rcd is required despite being already on cu-rcd circuit and some including you (perhaps) -- not , then this is the evidence of ambiguity (IMHO)

No it isn't, it is evidence that different people have different opinions on going beyond the requirements of the regulations.

Ask any one of those electricians to show you the requirement for a second 30mA RCD connected in series in the regulations and they will not be able to.
 

Reply to Whirlpool bath. Is there legal requirement for additional dedicated RCD even if we have Double RCD CU? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock