Discuss Why a separate earth for caravans in the UK Electrical Forum area at ElectriciansForums.net
Not tonight! I’m in proud dad mode as my teenage daughter has a gig and is doing great!What, you don't take your regs into the pub! Shame on you.
Technically yes, but many "TN-S" supplies are actually off segments with a PME conductor, just they look separate at the DNO cut-out.So if they have TNS or TT then I can use the installation earth?
The two issues with using the SWA armour are:Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?
Does anyone have a reply to this?So if they have TNS or TT then I can use the installation earth?
Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?
Yet again you have came to answer stuff. Thanks pcTechnically yes, but many "TN-S" supplies are actually off segments with a PME conductor, just they look separate at the DNO cut-out.
Personally I would TT it unless the main supply was already TT.
The two issues with using the SWA armour are:
See also this article:
- If using a 16A or 32A "commando" socket you will struggle to have any reliable connection to the armour. For hard-wiring to a fixed unit with glands no problem
- The end of cable Zs for disconnection has to be met. For TT supply (RCD before the SWA run) then no problem as RCD will disconnect on any sort of armour impedance, but if TN to the caravan point you ought to check it is met.
Electrical installations in caravan/camping parks, caravans and motor caravans
As the warmer weather approaches and with summer around the corner, thoughts turn to holidays. Chief Engineer Geoff Cronshaw reminds us of the requirements of BS 7671:2008+A3:2015.bit.ly
Sorry it's a static. And about 30m run I'm cableStill like to know if this is for a tourer or a static…. But the 10.0mm mentioned on #3 suggests something big.
How’s the wording of the regs on this?
I’m sure it says a rod for a caravan park, not for just a caravan plugged into a house…
So if they have TNS or TT then I can use the installation earth?
Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?
Reply to Why a separate earth for caravans in the UK Electrical Forum area at ElectriciansForums.net