Search the forum,

Discuss Wiring an additional PIR sensor in the UK Electrical Forum area at ElectriciansForums.net

T

TaffyBoy

I am in need of some help. I have a security light which has a built in pir sensor. I have bought and additional one that I want to wire in to cover an additional area at the front of my house.
The existing light has only two wires coming out of it, a live and a neutral, that go into a choc block fed from a mains switch in the house. Now the new standalone pir sensor has 3 wires from it into a choc block, live, L1 and neutral.
How to I wire it in?

Many thanks.
 
As described, you can't wire it to work as you'd hope.


You can only supply power to the stand alone PIR and that could trigger the other one (pretty pointless).
You need access to the wiring "further in"
 
Not with the wiring described, no. You need to be able to wire the new PIR in parallel to the PIR mechanism of the combined light & PIR. So that either PIR will switch the light on, presumably.

You'd also need to supply power to both units.
 
Nope, there's just a 3 core cable coming out from the inside of the house and that's it. I needed the 2 sensors as I wanted one to focus on my steps and the other to focus on my door step. I'm thinking it may just be easier to buy a solar pir light to light the one area and leave the existing mains powered light to illuminate the other.
 
it can be done taff but as spartycus says, you will have to get to the internal switched output from the inbuilt sensor
 
If I find that wire can I just connect into that line then and run it from the inbuilt sensor in the light to the L1 terminal in the standalone pir sensor?
 
it should be fine taff, all it is -is another switched contact in parallell you could add even more pir,s if you wanted too
 

Reply to Wiring an additional PIR sensor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
518
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
510
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
814
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
603
I recently purchased a LAP PIR sensor https://www.NoLinkingToThis/p/lap-indoor-outdoor-white-pir-standalone-sensor-360-/9695v I presently have 4...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock