Discuss Workshop power in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello can anyone offer and advice on running power to an workshop. All work will be done by a professional electrician, I am merely seeing if my idea is feasible. So far I have 6mm swa prysmian cable buried according to reg, sand bedded and warning tape over etc 6.5 metre run.
I have recently had a new electric oven installed which is 240v 2075w. I have an unused switched supply on the kitchen ring main for an old baseboard heater.
Would the following be possible, connect the over to the unused 13amp switch, use the oven supply which is a 32amp supply with a dedicated rcd in the main panel to power the workshop?
The total distance for the shed including the existing cooker feed is 16 meters.
I am planning to run the trunking for the internal cable when I rip out the kitchen.
As I said I will not be doing any of the electrical work and will get a professional electrician to do it but wanted to know if the concept will work or if I am missing something obvious.
 
Do you a electric hob? does it have its own 32A circuit ? if so, could the oven be connected to that circuit somehow as loads over 2kw (2000w) should be on a dedicated circuit.
 
Ideally you would run the SWA all the way from the garage to where your consumer unit is, and connect the SWA to a non RCD breaker, or preferably to a separate switch/fuse.
Always intrigues me why DIYers and some professionals always use the minimum amount of SWA necessary, and then join to T&E.
 
Ideally you would run the SWA all the way from the garage to where your consumer unit is, and connect the SWA to a non RCD breaker, or preferably to a separate switch/fuse.
Always intrigues me why DIYers and some professionals always use the minimum amount of SWA necessary, and then join to T&E.
Thanks, as I said I don't know so I thought I'd ask some people who do. Running to the consumer unit is going to be a huge mess so I guess this will have to wait for a while.
 
What is the loading (expected) for the workshop ....... it may be that the workshop connected to the 13A S/FCU might work?
 
What is the loading (expected) for the workshop ....... it may be that the workshop connected to the 13A S/FCU might work?
I will be running various power tools including, a table saw, vacuum for extraction etc. Possible heat in the winter so I was thinking I'd need a full 30amp supply. Light will be led all the other power tools are less than 2000w but cumulatively it all adds up.
 
What is the loading (expected) for the workshop ....... it may be that the workshop connected to the 13A S/FCU might work?
This is true for a light plus occasionally used 13A socket in a shed, but for a workshop as above it's really a non starter. Apart from the extremely limited load, the RCD and type 2 MCB in the house will be a pain to reset.
For that lot, I'd up the cable to 10mm2 SWA and 45A switch fuse.
 
This is true for a light plus occasionally used 13A socket in a shed, but for a workshop as above it's really a non starter. Apart from the extremely limited load, the RCD in the house will be a pain to reset.
Was planning to put a separate small consumer unit in the shed, but even so I think a separate feed is probably the only way to go. Just have to explain to the Mrs why I am knocking out the under stair area ?
 
CU with RCD or RCBOs in the workshop is the way to go, but there's no point fitting an RCD there if the power passes through another one in the house. That's a reason to use SWA all the way, so that the cable doesn't need RCD protection.
 
Is there any other route for the cable, even if it is run around the outside of the house?

Whatever you do, you might also think about having emergency lighting so if the power goes off for any reason you are not plunged in to total darkness with sharp tools around, etc. You get LED strip lamps with that built-in, so if you have at least one emergency LED baton out of 2-3 for the working light you would be a lot safer.
 
Do you a electric hob? does it have its own 32A circuit ? if so, could the oven be connected to that circuit somehow as loads over 2kw (2000w) should be on a dedicated circuit.
Do you have a regulation number DefyG I always thought it was just an advisory notification
 
Do you have a regulation number DefyG I always thought it was just an advisory notification
It's only mentioned in appendix 15 (informative) as far as I'm aware.
But probably a good idea to comply with it anyway, as the ring may already be somewhat fully loaded.
 
It's only mentioned in appendix 15 (informative) as far as I'm aware.
But probably a good idea to comply with it anyway, as the ring may already be somewhat fully loaded.
I agree why won't/don't the IET make it a regulation , make life easier for all concerned, don't you think?
 
I agree why won't/don't the IET make it a regulation , make life easier for all concerned, don't you think?
Because we're supposed to be 'competent persons' who should be capable of designing a circuit outside of the norms. In most cases, a 2kW+ fixed load shouldn't be connected to a RFC, but occasionally (e.g. very short duration load?) it may be acceptable.
 
Because we're supposed to be 'competent persons' who should be capable of designing a circuit outside of the norms. In most cases, a 2kW+ fixed load shouldn't be connected to a RFC, but occasionally (e.g. very short duration load?) it may be acceptable.
Agree but many Electricians want the rules and regulations in black and white, it wouldn't be to much to ask to point this out to the less educated newbies amongst our community would it?, maybe those that think they know it all will disagree. What do you think? I'm not including you in the know it all statement by the way.
 
I agree why won't/don't the IET make it a regulation , make life easier for all concerned, don't you think?
I guess the obvious answer is that it is not always a problem.

Usually rules & regulations always get bigger with time as the authors try and deal with each "WTF?" that an inquiry reveals, but as they become more prescriptive you end up with dumb things being done to follow the letter of the regulation, but without any understanding of why it might be needed (or not) and possibly causing other problems or risks.
 
Hello can anyone offer and advice on running power to an workshop. All work will be done by a professional electrician, I am merely seeing if my idea is feasible. So far I have 6mm swa prysmian cable buried according to reg, sand bedded and warning tape over etc 6.5 metre run.
I have recently had a new electric oven installed which is 240v 2075w. I have an unused switched supply on the kitchen ring main for an old baseboard heater.
Would the following be possible, connect the over to the unused 13amp switch, use the oven supply which is a 32amp supply with a dedicated rcd in the main panel to power the workshop?
The total distance for the shed including the existing cooker feed is 16 meters.
I am planning to run the trunking for the internal cable when I rip out the kitchen.
As I said I will not be doing any of the electrical work and will get a professional electrician to do it but wanted to know if the concept will work or if I am missing something obvious.
Hi,
Yes you can do it and I think that it's you who is a professional electrician, all what you've to do is to divide 2075w per 230v, you will find less than 10 ampers and it's exactly a value near breaker rating, 13 ampers, in the other hand, you have to set up an rcd upstream the breaker.
 
But in any event if you use the correct value of U0 it is less than 2kW.
The 2kW is only a nominal value at a nominal voltage, quoted by manufacturers as with voltage fluctuations or volt drop the output power could be less but could also be more if manufacturers base it on a nominal 230v and actual is 234volts!
 
The 2kW is only a nominal value at a nominal voltage, quoted by manufacturers as with voltage fluctuations or volt drop the output power could be less but could also be more if manufacturers base it on a nominal 230v and actual is 234volts!
But it's always been that way for resistive loads - they are quoted at a particular voltage or voltage range.

The correct voltage to use in calculations is 230, so loads should be evaluated on the basis of what they are at that voltage.

new electric oven installed which is 240v 2075w.

So it should be viewed as 1906W.

I don't think you'd get many takers for the view that a 1700W appliance should be put on a dedicated circuit as it would be over 2kW at 253V.
 
Agree but many Electricians want the rules and regulations in black and white, it wouldn't be to much to ask to point this out to the less educated newbies amongst our community would it?, maybe those that think they know it all will disagree. What do you think? I'm not including you in the know it all statement by the way.
Some counties have Regs imbedded in the law and their Regs are very specific about compliance with prison sentences for when it goes wrong. I was working in one such country when I took their Regs course and we were told at the time there were 4000+ electricians facing prosecution.
 
Send them off to get a left hand screwdriver and a tin of current
Dont jest, this website has 3922 of them apparently ?

1618048412865.png
 
I sometimes wonder why folks get so worked up about the "2kW fixed load" thing.

We all know the RFC is quite robust and tolerant of most things and many houses have (or had) practically everything bar the lights & cooker on a single RFC. Quite often folks would have a couple of 3kW heaters and the usual washing machine, tumble dryer, etc, in use and no problems.

Putting significantly more than 13A on at a point on the RFC is getting in to suspect territory as you can't be sure of how well the currents in the two "legs" are going to balance, but we have few loads that come in to that area. Probably just wired-in cookers, heating showers, or an EV charger in recent year or two, and they would normally be on separate radials anyway.

The only odd one I can think of is the old immersion heater, less popular these days due to combi boilers and instant-heat showers, as they would typically be around 3kW and could be heating for an hour or more easily. So were they the motivation for saying fixed loads above 2kW, and not the 3kW of a 13A socket?

Also the argument for putting something on to a separate circuit goes beyond the basic aspect of circuit protection alone, there is also the "good engineering" aspect of minimising inconvenience/risk under fault conditions to allow the fault to be isolated with the least collateral damage. I guess a number of "fixed loads" come in to this sort of territory, especially water heaters, where you would want to be able to keep any faults from taking out all/half of the house socket outlets as well.
 
I sometimes wonder why folks get so worked up about the "2kW fixed load" thing.

Quite often folks would have a couple of 3kW heaters and the usual washing machine, tumble dryer, etc, in use and no problems.
This is exactly why! The above may well work on a single RFC with no problems in practice, but if there's a 2kW+ fixed load as well, that will likely take it over the edge.
 

Reply to Workshop power in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
712
Hi, I am Currently in the process of building an extension and my builders will shortly be getting their electricians to commence the first fix...
Replies
6
Views
445
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
948
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
623
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top