hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?
Discuss Zs on tt in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hi all am i right in saying on tt systems the Zs reading will be a lot higher than the max? and is this exeptable?
say the Zs on a ring main is 3.45ohms or higher on a TT are u saying 1667ohms is the max?
As Zs=Ze+R1+R2 then yes Zs on a TT system will generally be much higher than a TNCS system.
The maximum values are given for TNCS systems and therefore are not applicable to TT systems. The maximum value given in BS7671 is, I believe, 1667 ohms.
does this 1667ohms mean the max for all mcb sizes? o and what does IMO mean always wondered
was about to say as widdler max. touch voltage 50 so 50/0.03mA = 1666 recuring rounded to 1667, but OSG says anything over 200 ohms should be considered unreliable due to soil drying out ect.
TT probs with B.Gas 'engineers' having plug in Go/noGo testers for supply to boilers having fail setting of a couple of ohms, trouble is they are always taught on TNS systems and don't understand TT.