Teddy54

Hi Iam working on an outdoor public toilet and my zs readings to the circuits are in the range of 62 to 68.5 ,wereas on other simalir units it's been 0.5 - 0.7 . I have ensured all terminations are tight and belled out all circuits to ensure proper earth. It's a tns system. My ze PFC are fine. Any suggestions on what could be causing such a high reading?

Regards
Teddy
 
How are you taking this Zs by measurement I guess.

Is there an RCD on the circuit and could you be getting a false reading via the soft test.

You could also be getting a false reading if doing the full Zs no trip test through an high impedance of an MCB.

Personally I would do an R1 + R2 on the circuit to see what that is telling me. If that is within the expected levels, then test re-test with another type of MCB in the circuit.
 