Currently reading:
Zs readings

Discuss Zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

stu35

Hii all I am pretty new to this job and was wondering if somebody could just give me some advice on Zs readings?

What would be most likely the cause of high Zs reading's say on a cooker or sockets circuits if Ze is ok?

Thank you all advice appriciated:)
 
Well the first thing to consider is how do they compare to the R1+R2 readings for the circuit in question.;)


A high impedance could be caused by a number of things.....circuit length, size of conductor, poor conductor terminations/high resistance joints.
 

Reply to Zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top