Search the forum,

Discuss Zs testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
1
Evening all.

Is there a regulation or any guidance regarding live zs testing with loads connected....

Eg zs testing on a 3phase motor whilst it is running. Could the current being drawn damage the meter if testing at the end of line.... Or doing a live zdb test, is there any guidance to say there must be no live loads or a maximum current being drawn at time of test ?

I hope this makes sense I am new to testing and don't want to damage my mft1730 Megger.

Thanks
 
The running motor won't damage your MFT but it can lead to a higher than expected PSCC as the motor has inertial and on slowing works as a generator. As a result it is not really giving you the circuit's Zs value for fault clearing at the supply, since you have in effect a 2nd power source nearby.

In some larger systems where you are trying to work out max fault currents (either for checking MCCB/fuse/switch limits, or arc-flash safety calculations) then the contributions of nearby motors can be significant, at least for a few cycles of the AC as its magnetic field collapses (or it stops, probably later).
 
Last edited:

Reply to Zs testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
664
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
900
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
13
Views
4K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock