Discuss Zs / Ze 1720 confusion in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Can anyone advise or explain the correct procedure to carry out the above tests on a megger 1720?
I recently purchased a megger 1720 and thought I would have a play with it at home before taking it on site. When carrying out z tests it give you a choice of 2 and 3 lead hi and low test all giving you different results I had a quick look in the distractions but thought you guys and girls may have a bit more experience and be able to explain in pracical terms.
 
I have an MFT 1731.

For Ze (for measuring Ze, PEFC and PSCC) you should use the two lead hi current mode. For Zs you should aim to use the two lead hi current test if the circuit is not RCD protected and the three lead low current test if it is.

The three lead low current test is not as accurate as the two lead hi current, but it shouldn't trip RCDs (which can adversely affect the test results which is why you'll find information in various threads here about bypassing RCDs and using the two lead hi current test).

Hope that helps.
 
I have the Megger 1741 however I used a Fluke in the past and they are both perfectly good testers and the Minions have been done to death in merchandising. The instructions should be useful regard both "LO" and "HI" tests for L-E and L-N.
 
Yellow has been made a little more cool by the
"Minions"
yeah ,but made by this guy.
upload_2018-1-17_15-17-33.png
 
meggers bfore the 1700 series used to need 3 wire test for no trip. just bear in mind that, due to the much lower current used in any no-trip test, the results may not be accurate due usyally to some contact resistance which is overcome when performing a hi current test.
 

Reply to Zs / Ze 1720 confusion in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock