Search for tools and product advice,

Discuss 60947-2 MCCB...........what type? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

mcvee

I cant seem to find a definate answer to what type would a 60947-2 MCCB be when generally a 60898 mcb is b,c or d.
I have the manufactures data for max zs values on the mccbs, but I need to know the type to complete a schedule of circuit details.

Cheers
 
thanks for that, thats a helpfull bit of info, Ill save the pdf.

Could anyone clarify the following;

So it seems there is categories A & B, Im i right in thinking a' Cat A' MCCB is the older bs 4752 and the newer 60947-2 is 'Cat B'?
Or is it that a 60947-2 on a sub main feeding a DB would be 'Cat A' & a Main incomming 60947-2 would be 'Cat B'?
 
thanks for that, thats a helpfull bit of info, Ill save the pdf.

Could anyone clarify the following;

So it seems there is categories A & B, Im i right in thinking a' Cat A' MCCB is the older bs 4752 and the newer 60947-2 is 'Cat B'?
Or is it that a 60947-2 on a sub main feeding a DB would be 'Cat A' & a Main incomming 60947-2 would be 'Cat B'?


I'll think you'll find the difference is, that one type of MCCB is non discriminating and the other type is... The type that discriminates will be provided with time delay, adjustable trip settings etc!!

MCCBs/ACBs/GCBs do not come in categories as like MCB's.... For the main, they achieve, discrimination by variable parameters, depending on the model make and the system they are installed within.

If you have the manufacturers data there as stated for Merlin Gerin, it will tell you exactly what MCCB you will need for protecting MCBs types and or other MCCBs...
 
I am not totally sure but you mentioned Merlin Gerlin and me thinks these have adjustable settings on them


No... not all of Merlin Gerins MCCBs will have adjustable settings. Those MCCBs that just need to protect the downstream MCBs from high PFCs for arguements sake, will not need, or have adjustable settings included in the frame.
 

Reply to 60947-2 MCCB...........what type? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello All. New here and will be flooding with terrible questions for my own knowledge. Just trying to learn so some questions like this maybe very...
Replies
6
Views
1K
I have seen recent changes that require (most) EV chargers and solar systems to be fitted with a type B RCCD. I work with power semiconductors...
Replies
9
Views
1K
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
800

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top