Discuss What would explain this strange measurement in the kitchen? in the Canada area at ElectriciansForums.net

Reaction score
0
In the breaker box of a 2010 house, there is a distinct 15A breaker for the garburator and distinct 15A breaker for the dishwasher.

The garburator is powered only if the garburator breaker is on.

But the line to the dishwasher is powered if EITHER the garburator breaker or dishwasher breaker (or both) are on. What would explain this?
 
In the breaker box of a 2010 house, there is a distinct 15A breaker for the garburator and distinct 15A breaker for the dishwasher.

The garburator is powered only if the garburator breaker is on.

But the line to the dishwasher is powered if EITHER the garburator breaker or dishwasher breaker (or both) are on. What would explain this?
There's an incorrect link between the two breakers.
 
The OP is Canadian, it could be a link on one side of a split-phase breaker, with one load on the L1-L2 @ 240V and the other on linked L?-N @ 120V.
 
In the breaker box of a 2010 house, there is a distinct 15A breaker for the garburator and distinct 15A breaker for the dishwasher.

The garburator is powered only if the garburator breaker is on.

But the line to the dishwasher is powered if EITHER the garburator breaker or dishwasher breaker (or both) are on. What would explain this?
The best way I can say is that the dishwasher and garbage disposal both require their own separate circuit.
 

Reply to What would explain this strange measurement in the kitchen? in the Canada area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
497
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
733
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
225
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
496
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock