Hi folks

I've just identified as cause of lighting circuit tripping in consumer unit a low volts ceiling light with laride transformer taking in 240V 50Hz and output 12V 60VA with load 3 LEDs rated at 2.4W/ 300mA. This unit is only a few years old and not much used. What kind of lifetime should be expected for these?

The transformer now has continuity between input line and neutral. Certainly explains the trip. I don't know about transformer failure modes. Is this one typical? Are there any source for a replacement transformer anyone would recommend?

Thanks
 
A transformer's life is indefinite provided it hasn't been over loaded or allowed to over heat by enclosing it and not giving enough free air to dissipate heat.
 
Thanks

Kindof what I thought, too.

This one, with the stated load (or previous 10W halogens) is used to light the stairways for as long as it takes to walk up or down them. Its installation is flat to ceiling in a vented enclosure, presumably of lamp-makers design.
 
Is it a transformer or a driver? If the latter, are you above its minimum load requirements now that you have fitted LED lamps?
 
From line to neutral resistance is exactly nil ohms

Interesting. Sounds unusual since it seems it was very lightly loaded. Not much you can do I suppose other than buy a replacement unit.

Unless you fancy removing the covering and checking the windings.
 

Reply to Laride transformer failure query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
475
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K
I recently had some landscape lighting put in and wanted to hook up the transformers to a smart plug so I can control them with my phone and have...
Replies
2
Views
2K
Evening peeps, Got a question i need help with a friend of mine has an american food processor the unit is 1000w 110v i purchased a 3000 w 230 to...
Replies
18
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top