Search the forum,

Discuss PME system with earth rod aswell in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Gavin John Hyde

-
Esteemed
Arms
Patron
Reaction score
5,173
Been on a job today and debating what to put on the certificate.

The DNO in early 2013 upgraded the supply and installed PME. The previous setup had an earth rod installed. This is still connected to the main earth terminal. Not sure what type the previous set up was as the customer is none the wiser, As the upgrade was done just before she bought the house.all she cared about was that things come on and turn off when required.

I am only filling in a minor works certificate as it only involved extending a radial.

In terms of earthing arrangement would you all agree i have been okay to record it as PME with a supplementary TT rod. making a note in the comments box mentioning there is a rod aswell? Guess it will be 18th edition compliant before its time!

I have so far filled it in as a PME system and am wondering if in addition to recording the Ze of 0.29 ohms i should record Ra aswell? I haven't measured it as of yet as i went with its a PME with supplementary rod.

I have to go back Monday next week to change a light fitting, so can measure Ra if needed.

It does raise the prospect of whether the certificate forms will be updated to reflect 18th edition if supplementary rods are going to be needed.

Thoughts welcome as it is something I haven't dealt with or potentially noticed before as most of my experience is light commercial such as pubs.
 
If it's been changed to pme then why bother with the earth rod?
By definition from the DNO having Carried out works it's a TN-CS earthing arrangement
 
i'd just do as you suggest. record Ze and PME earthing , with a note saying there is a supplementary rod.
 
I imagine the younger people reading would see @Pete999s' comment "Diss the rod" as
That is a crap rod and looks bad innit, nowadays:cool:
i know me and pete are both old coffin dodgers, but surely you can tell us apart. i'm the good looking one. :p:p:p
 
It's TN-C-S. The fact it also has an Earth rod is irrelevant (in fact, it is a very good thing). No need to worry about Ra of the rod.

Most of the rest of the world requires Earth electrodes on TN-C-S installations - it's about time JPEL/64 caught up.
 

Reply to PME system with earth rod aswell in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just watched one of John Ward's interesting videos - It all makes sense apart from one of the final points involving adding an earth rod...
Replies
24
Views
4K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
I am considering the options which may apply to the earthing arrangement for a supply to a wooden shed. The property has a TN-C-S supply from...
Replies
8
Views
4K
Hi. New to the forum. I hope I've chosen the correct category to place my post. I tested a landlords property recently, turned out to be TNC. I...
Replies
14
Views
2K
A quick search for earth tape didn't come up with much, though this thread was of interest. I'll start by mentioning that I've led a sheltered...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock