if it was me, i would use an individual box for each and use the piranha nuts for each gland to give yourself the best chance of keeping you Zs down
 
Electric Intake 3.jpg
Slight revision, Cut-Out is slightly bigger, I've also set meters directly on trunking to reduce overall height and lift lower switchfuses.

UKPower Networks and EDF have both approved design, but I would be greatful of any further suggestions.

Thanks
 

Attachments

  • Electric Intake 3.jpg
    720 bytes · Views: 44
Last edited:
Looks good and well thought out, however supporting and terminating the SWA's into the 110M's is going to be tight

Also have you confirmed that a 10m clearance on the bottom of the Ryefield is ok with the DNO
 

Reply to Terminating SWA with Wylex REC Supply Isolators in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
903
I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
845
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
782
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock