C
Chris14
For 11kw shower what cable size is required for 15m run?
Discuss 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net
I'm in the gaggle seats but not in that list
i need to know if i used 11kw 3phase motor 380v, what size of cable can i use?11kW @ 230V = 47.8A
11kW @ 240V = 45.8A
Whichever way you look at it 6mm² will not be sufficient because the CPD will need to be a 50A MCB as Tel has already stated.
You need to state how the cable is run however, because the environment the cable is installed in dictates how much it is de-rated by, and you could end up with 16mm² if your running it in fully insulated spaces or in an environment subjected to external heating.
Oianyone living next door to the jones's who have a 10kW shower. just plain snobbery.
Reply to 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net