6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation. 10mm on a 50AMCB is your only choice.
 
11kW @ 230V = 47.8A
11kW @ 240V = 45.8A

Whichever way you look at it 6mm² will not be sufficient because the CPD will need to be a 50A MCB as Tel has already stated.

You need to state how the cable is run however, because the environment the cable is installed in dictates how much it is de-rated by, and you could end up with 16mm² if your running it in fully insulated spaces or in an environment subjected to external heating.
 
Guys, what about this kiddy...

Redwing 12kW Shower

Personally I say 16mm² will be sufficient on a 286m run, but the Regs work it out to be a 120mm²...anyone any thoughts...Muhahahahahaha :D
I got asked to install one of those once and his "mate" who was an electrician but out of the country at the time said it could be spurred off the ring :D i couldn't see a problem and i only had 1.5 with me at the time so i used that, do you think it'll be ok? I did change the mcb to a 50A too cos it kept tripping that poxy 32A :D
 
Christmas day mum has the cooker going full pelt and dad decides to make her a cup of tea and a slice of toast and at the same time daughter steps into the 11kw shower thats when you find out if your 60A DNO fuse will be ok lol
 
The OP occupation is stated as Gas so at a guess he's either got bad wind or he's a plumber and with all due respect to the kind nature of this forum he really needs to get a competent electrician on site as oppose to taking a few tips off here and doing it himself, any missed info could be vital to the safety of this install and he clearly hasn't any electrical experience with the basic form of his question...... do the OP a favour boys and recommend a sparkie to weigh it up you haven't spent years training and learning all this to do all the calcs for a DIYer /plumber working outside his trade.
 
Dare I venture to suggest getting a sparky in?

Or has the OP gone away?????????

I think I found him..

finger-in-socket-1.jpg
 

Reply to 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock