6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation. 10mm on a 50AMCB is your only choice.
 
11kW @ 230V = 47.8A
11kW @ 240V = 45.8A

Whichever way you look at it 6mm² will not be sufficient because the CPD will need to be a 50A MCB as Tel has already stated.

You need to state how the cable is run however, because the environment the cable is installed in dictates how much it is de-rated by, and you could end up with 16mm² if your running it in fully insulated spaces or in an environment subjected to external heating.
 
more like apocolypse now. wait for the 10kW cooker cable questions.
 
Guys, what about this kiddy...

Redwing 12kW Shower

Personally I say 16mm² will be sufficient on a 286m run, but the Regs work it out to be a 120mm²...anyone any thoughts...Muhahahahahaha :D
I got asked to install one of those once and his "mate" who was an electrician but out of the country at the time said it could be spurred off the ring :D i couldn't see a problem and i only had 1.5 with me at the time so i used that, do you think it'll be ok? I did change the mcb to a 50A too cos it kept tripping that poxy 32A :D
 
Some of these showers are turning mental, it's got to get to a point when you can't really heat the water much quicker under standard water pressure?
 
anyone living next door to the jones's who have a 10kW shower. just plain snobbery.
 
Christmas day mum has the cooker going full pelt and dad decides to make her a cup of tea and a slice of toast and at the same time daughter steps into the 11kw shower thats when you find out if your 60A DNO fuse will be ok lol
 
The OP occupation is stated as Gas so at a guess he's either got bad wind or he's a plumber and with all due respect to the kind nature of this forum he really needs to get a competent electrician on site as oppose to taking a few tips off here and doing it himself, any missed info could be vital to the safety of this install and he clearly hasn't any electrical experience with the basic form of his question...... do the OP a favour boys and recommend a sparkie to weigh it up you haven't spent years training and learning all this to do all the calcs for a DIYer /plumber working outside his trade.
 
Dare I venture to suggest getting a sparky in?

Or has the OP gone away?????????

I think I found him..

finger-in-socket-1.jpg
 
I have a 43.9kW shower...well actually it's a 150,000 BTU Potterton Boiler...That is only wired on a 1.5mm² flex from a 13A spur, works fine!! (I think the gas connection helps though!)

It will do more than work fine ... It'll knock the spots off any domestic electric shower any day of the week, any time of the year.
 
The same loony who surprises you with an 11 kw range oven with induction hob, warming draw twin oven and grill after saying its a double oven and gas hob......

Bit of 6mm and a 32 it is, then. ;)
 
My 8kw serves me well, usually use it on half power setting as well. Still miss the power shower from the old house though. And my 8kw is on 10mm and a 32a breaker for info :)
 
6mm clipped direct just on the limit, but you'd need a OCPD of 50A, so 6mm is out of the equation.
Why?
433.3.1 (ii)
A shower is a fixed resitive load, so very unlikely to be subject to overload current apart from a fault.
It has fault protection via the RCD (and the 50A CB), any fault will be cleared in less than 0.3 seconds that the RCD takes, so a 50, or even 100A CB will be compliant.
(of course so long as cable length, Zs, grouping/reference all comply too)
 
the shower is 47A so the OCPD needs to be >47A but less than the Iz of the cable. so a 50A MCB. this means that the cable Iz must be > 50A so it's got to be 10mm.


what's the RCD got to do with overload protection?
 
No, sorry, you are wrong.
It is a fixed resistive load, so does not need overload protection, it must have fault protection, which the RCD will provide.
 
nothing to do with the type of load. it's the cable that needs overload protection. what's the RCD going to do in the case of a short circuit L-N?
 
433.3.1
There is no need for circuit protection if the load is unlikely to carry overload currents. A shower will not overload unless it has a fault. No-one is likely to fix the circuit directly to the outgoing RCD terminals, so fixing it to a CB rated higher than the current carrying capacity of the cable is quite acceptable in such circumstances, so long as the cable can carry the current of the appliance.
A L-N fault will cause many hundreds of amps to flow (in most installations), meaning any CB fitted, whether 50 or 100A will trip virtually instantly. It is only in fault conditions that a L-N short will occur.
Hence it is compliant to run a cable with a 47A capacity, feeding a 45A fixed load appliance, fed via a 50A CB, as there will be fault protection, both via any CB fitted, and via the RCD which will have to be fotted in any domestic premises. There will be no overload protection, but that isnt required, as stated in 433.3.1.
 
i'll accept that if , and only if, the circuit Zs is sufficiently low enough to cause the OCPD to trip within the required time. e.g. < 0.37ohms for a 100A type B MCB. say the Ze was 0.2, then your R1+R2 for the 6mm cable would need to be < 0.17, i.e a circuit length of not more than 15m. if the Ze was > 0.3ohms, then you're stuffed.
 

Reply to 11kw shower cable size? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi , I’m going install a commercial 450mm extractor fan , what size and type of cable should i use ?
Replies
7
Views
459
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
685
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
1K
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
542

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock