Hello all. I am having an issue with a 12V DC Relay I am trying to install to run a kill switch on a John Deere Diesel engine that runs a high pressure water pump. I have the relay wired in such that it will send power to the ignition when an electrical signal comes from a water sensor in the pump (dry running protection). The issue I have is that whenever it is hooked up all I get is chatter from the relay. I have tested my wiring by connecting the "switch" wire to battery and everything works as it should. I read somewhere that if the switch voltage is less than the feed that it can cause chatter. The fees voltage is 12.56 and the switch voltage is 12.22. Could this be the reason and how should I go about fixing it? Thanks
 

Attachments

  • 15615585866361309218059.jpg
    970.8 KB · Views: 29
So the signal from the water sensor is ok then and this is not causing the relay to chatter?
 
I presume you don't have a variable power supply. To feed 12.22v from this to the relay and still see if you get chatter...
 
A 12V relay will usually pull in around 8-9V on the coil, and will hold in down to about 6V. Anywhere between 9 and 18V should be OK, it is not critical. There is no relationship between the coil voltage and the contact switching voltage. Probably, the sensor output is not giving a steady voltage, or there is a bad connection somewhere, or the relay is not actually a 12V relay.
 
A 12V relay will usually pull in around 8-9V on the coil, and will hold in down to about 6V. Anywhere between 9 and 18V should be OK, it is not critical. There is no relationship between the coil voltage and the contact switching voltage. Probably, the sensor output is not giving a steady voltage, or there is a bad connection somewhere, or the relay is not actually a 12V relay.
Okay thanks. I will check with the sensor manufacturers and see if it is constant or not to double check. If it isn't, is there anything that can be done or a different style relay to use?
 
What type of output does it have - contact closure, open collector? Is it designed to operate a relay or just trigger an electronic input of a system controller?
 
It is grounded to a point on the frame of the unit. When it senses the water it closes a circuit with the power feed to send power down the switch wire. I think it is designed to be used in a system controller but the dealer said people have used it to operate a relay.
 
What is the kill switch connected to out of interest. Is it to disable the ignition or the fuel pump .
Sorry I may have worded it wrong before, there is no actual kill switch. The relay acts as the kill switch. The ignitions power flows through it so if it ever switches off then the whole engine control unit goes dead and it shuts down fuel as well. I have tested the function of the relay and just used an alternate power source as the switch instead of the sensor and everything works as it should.
 
We
Sorry I may have worded it wrong before, there is no actual kill switch. The relay acts as the kill switch. The ignitions power flows through it so if it ever switches off then the whole engine control unit goes dead and it shuts down fuel as well. I have tested the function of the relay and just used an alternate power source as the switch instead of the sensor and everything works as it should.
Well done . :)
 
Sorry I may have worded it wrong before, there is no actual kill switch. The relay acts as the kill switch. The ignitions power flows through it so if it ever switches off then the whole engine control unit goes dead and it shuts down fuel as well. I have tested the function of the relay and just used an alternate power source as the switch instead of the sensor and everything works as it should.
It sounds like, as I think Lucien was suggesting in post #12, the sensor cannot supply enough current to operate the relay, causing the voltage to drop and make it chatter.
 
Maybe the sensor produces pulses instead of continuous DC, either because it works that way or because the water flows in pulses. If you can get hold of an oscilloscope or scope meter it would be worth checking that the sensor output voltage isn't jumping around.
If it is DC but doesn't have enough current drive for the relay then a solid state relay may work, they work on small drive current over a wide voltage range but would need to be one made for DC loads, many are for AC only.
Out of interest, did you measure the sensor voltage with the relay coil connected?
 
I would look at using a ready built relay module which has a transistor driving the coil of the relay. This is more likely to work with the possibly weak output of the sensor. They would usually take the form of a circuit board with a handful of components pre-assembled and should be available from ebay or other web sources.

Obviously this would want mounting in a little ABS project box.

You could have got one from Maplins up until last year sadly.
 
The pump may not be giving smooth pressure, it may be more like a series of rapid pressure pulses which is causing the sensor to give an output that isn't smooth which in turn is causing the relay to chatter.

The sensor might not be particularly well suited to this application but it might work if you can build in a delay somewhere in the system such as a relay with a magnetic 'slug' built into it which makes it slower to release.
 
Hello Everyone. Thanks to all who replied with helpful comments and solutions. I just wanted to update that work has been busy and we had to move off of getting this problem fixed but in my spare time I managed to find out that the sensor does not send a constant feed and is causing the relay to chatter. I will be talking to the manufacturers to see if there is a way to re program it or a different option. Thanks again
 

Reply to 12V DC Relay Issues (Diesel Engine) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top