Search the forum,

Discuss 12v Downlights causing other lights to turn on/off in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I've just noticed an odd problem.
I have 2x 12v downlighters in a small room.
On the same circuit, in my living room there are 12x 12v downlighters connected to two dimmable transformers.
The attached load is well within the limits of both the transformers and the dimmer switches that control them.
Sometimes, when the 2x 12v ligths are switched on the 12x 12v lights briefly turn on and off.
Any idea what might be causing this?
I was thinking possibly a defective transformer with the inrush causing the other 12x lights to turn on/off.
 
I would check all the connections at the JBs myself , if you have a poor connection this could cause a momentary loss of of supply either by neutral or the live , The LV tranys don't like voltage drop especially electronic ones
 
I would check all the connections at the JBs myself , if you have a poor connection this could cause a momentary loss of of supply either by neutral or the live , The LV tranys don't like voltage drop especially electronic ones

Just had another read and the 2 trannys that are possibly causing the problem could be temporally disconnected maybe and connect a couple of temporary pendants , thats another thought anyway..
 
could it be induced voltage with cables running together?
 
I wouldn't think it's an induced voltage.
Defective transformer is the likliest cause I reckon.
I haven't had time to check much further but I haven't been able to repeat the fault since I first witnessed it.
 

Reply to 12v Downlights causing other lights to turn on/off in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock