Search the forum,

Discuss 25mm and 16mm tails in same Henley block? in the UK Electrical Forum area at ElectriciansForums.net

D

don Logan

Hi, i've ran a radial into an extension. There are no spare ways on the existing 3036 DB. All the circuits are doubled up in fuse holders anyway and i want to leave that board well alone.


I'm gonna put a new 2 way DB in to feed this radial.

The existing board is fed in 25mm tails straight from meter.

Main fuse is 80amp, so i want to use 16mm tails as they will fit into a tiny DB a lot easier. Also 25mm is blatant overkill for a 2 way DB.

Only thing is, i would need to cut into these 25mm tails to add a DP Henley block and then have 16mm tails coming off of the Henley block to the new DB.

Is it ok to use 16mm tails when taking a feed from a Henley block fed in 25mm tails?


No 'I hope you're Part P registered and are going to declare this work' replies please. I'm a big fully qualified boy.

Thanks.
 
nothing wrong with what you intend, IMO.
 
As long as the load and OCPD in your new CU cannot exceed the capacity of your 16mm tails then you'll be fine, regardless of what your main fuse is (as long as it's within 3M of the supply)
As you will need to get your DNO to pop the fuse for this work, it may be worth getting them to simply fit an isolator, then you can do it all at your leisure.
Finally, as you are part P registered, it's always nice and easy to put questions like this to your scheme provider. A quick 2 minute phone call is always preferable to waiting around for an answer in here. :)
 
As long as the load and OCPD in your new CU cannot exceed the capacity of your 16mm tails then you'll be fine, regardless of what your main fuse is (as long as it's within 3M of the supply)
As you will need to get your DNO to pop the fuse for this work, it may be worth getting them to simply fit an isolator, then you can do it all at your leisure.
Finally, as you are part P registered, it's always nice and easy to put questions like this to your scheme provider. A quick 2 minute phone call is always preferable to waiting around for an answer in here. :)
oh come on!!...lol...
 
I usually do a risk assessment and find the DNO weren't needed.

Don Logan? Wouldn't want to get on wrong side of you I might find you stamping on my head when in bed in Spain.
 

Reply to 25mm and 16mm tails in same Henley block? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
322
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock