Currently reading:
25mm and 16mm tails in same Henley block?

Discuss 25mm and 16mm tails in same Henley block? in the UK Electrical Forum area at ElectriciansForums.net

D

don Logan

Hi, i've ran a radial into an extension. There are no spare ways on the existing 3036 DB. All the circuits are doubled up in fuse holders anyway and i want to leave that board well alone.


I'm gonna put a new 2 way DB in to feed this radial.

The existing board is fed in 25mm tails straight from meter.

Main fuse is 80amp, so i want to use 16mm tails as they will fit into a tiny DB a lot easier. Also 25mm is blatant overkill for a 2 way DB.

Only thing is, i would need to cut into these 25mm tails to add a DP Henley block and then have 16mm tails coming off of the Henley block to the new DB.

Is it ok to use 16mm tails when taking a feed from a Henley block fed in 25mm tails?


No 'I hope you're Part P registered and are going to declare this work' replies please. I'm a big fully qualified boy.

Thanks.
 
As long as the load and OCPD in your new CU cannot exceed the capacity of your 16mm tails then you'll be fine, regardless of what your main fuse is (as long as it's within 3M of the supply)
As you will need to get your DNO to pop the fuse for this work, it may be worth getting them to simply fit an isolator, then you can do it all at your leisure.
Finally, as you are part P registered, it's always nice and easy to put questions like this to your scheme provider. A quick 2 minute phone call is always preferable to waiting around for an answer in here. :)
 
As long as the load and OCPD in your new CU cannot exceed the capacity of your 16mm tails then you'll be fine, regardless of what your main fuse is (as long as it's within 3M of the supply)
As you will need to get your DNO to pop the fuse for this work, it may be worth getting them to simply fit an isolator, then you can do it all at your leisure.
Finally, as you are part P registered, it's always nice and easy to put questions like this to your scheme provider. A quick 2 minute phone call is always preferable to waiting around for an answer in here. :)
oh come on!!...lol...
 
What size are your MCBs in the new 2 way? If for example a 20A and a 6A there'd be nowt wrong with 4mm tails for your supply :)

Personally, I'd say even 16mm for a little 2 way is overkill (depending on circumstances obviously).
 
well then you should know the answer, an apprentice could answer this with a belly full of beer on board, come on man get a grip, what do you think :rofl:

I think yeah it's fine. But then I think of all the naysayers that might start saying that you can't mix conductor sizes without fusing down, even in a Henley block.

So I thought I'd ask. Seems a pretty valid question to me.
 

Reply to 25mm and 16mm tails in same Henley block? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top