Currently reading:
3 Phase 400 Volt K.E.M Isolator Earthing SWA

Discuss 3 Phase 400 Volt K.E.M Isolator Earthing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A

AssuredElectric

Hello u bright sparks!!

Right iv been given a job this week wiring up a car ramp in a garage. This is on a 3 phase 400 v supply.
(this is only my second go at 3 phase)

Im going to be using 6.00 mm 4 core SWA cable and K.E.M Heavy duty isolators, to distribute the power.

My question is regarding earthing.. in the passed when earthing SWA i have terminated to a c.c.u and earthed the earthing lug from the earth bar.

As i am terminating from a K.E.M (and have never worked with these before) where do i pick up my earth from? what size earthing conductor should i use?

Cheers :)
 
Are you talking about the Rotary plastic type KEM isolators?

Your saying you taking a 4 core 6 mm I assume that this will be the 3 phase and neutral, as surely the ramp control system will need a neutral, so your CPC is the armoured?

Personally I would terminate the armoured into a Galv 4x4 or 4x6 box and then pick up your earth via your banjo/earth nut as normal
 
the K.E.M's have rotary isolation handles on them, as iv never worked them before i dont know much more.

yes i will be using 4 core,3 phase 1 neutral but in regards to earthing the armoured (like i said in the passed iv only terminated to a c.c.u) so not sure how to earth glanding kit Lug? as to earth the armoured in needs to be connected to earth somewhere right? or am i confusing myself?? lol
 
Yes you seem to be confusing yourself yes.

This is a new circuit I take it. So your running you 6mm armoured from a Distribution board to the KEM isolator.

As your armoured is the CPC you need to gland and fit either a banjo/earth nut at your DB and then take a fly earth, 4/6mm to the earth bar in the board.

Then at your KEM, gland the SWA and again using a banjo/earth nut fit a fly lead to the KEM earth bar. Now if it's a plastic KEM as I said I would terminate the SWA into a Galv adaptable box, and then run tails and earth into the isolator
 

Reply to 3 Phase 400 Volt K.E.M Isolator Earthing SWA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock