Discuss am2 resit tommorrow swa/ sy earthing in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
1
resitting Saturday my am2 4 sections a3/b/d/e
swa and sy failed on protective conductors on both
swa i under stand thats the earths i think i used a smaller fly lead from the banjo to the db/ and a earthing nut with the banjo
sy think i used a 1.5mm flylead
so correct me if im wrong
the earth has to be the same size or bigger than the swa core size yellow lug
using the earthing nut no banjo required
 
in the day of 2c cable we used the same size earth fly lead as the line cores never bothered to work it out
 

Reply to am2 resit tommorrow swa/ sy earthing in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

attempted the am2 march 2022 passed A1/A2/A4/A5/C had a lot going on at the time death in family so never got back on this i have till march 24...
Replies
3
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
thinking now am2 is all about making money from people right i have left resits 1 swa and sy 2 knowledge exams 3 testing 4 faults passed the...
Replies
1
Views
1K
hi all new member from essex sat my am2 1 months ago passed ring /lighting/carbon dioxide/bonding /data/ safe isolation /risk ---...
Replies
0
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock