Discuss What crimp for 10mm fly lead to earthing nut ? in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
1
Hi,
I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the earthing nut (using 10mm to match the line conductor size as is good practice). Can't find any ring crimps that will take 10mm cable but have a lug hole small off to go on the earthing nut screw. Any ideas where to get one ?
thanks
 
Is the armour being used as the CPC or is the flylead just there to earth the armour?
If your just earthing the armour then a 6mm would be fine.

The screw in a 20mm earthing nut is M4 and a standard 10x6 lug can be persuaded to sit properly under it.
In this case its just for earthing the armour which is not used as the cpc. But the earthing of the armour is required to be able to handle the full fault current and although I'm sure 6mm would be fine a lot of the time if table 54.7 is used (rather than doing the adiabatic calculation) then the fly lead should be the same size as the line conductor so 10mm is the requirement here. I can't think that this is so unusual so I'm surprised that 10mm lugs with small (M4) holes are not widely available.
 
Is a longer M4 screw and 2 * 6mm in parallel an option using the typical yellow crimps?

Or even a 2nd M4 short screw and using another tapped hole on the earthing nut?
 
Or use an banjo and m6 screw and nut for the larger cables.
Keep the earthing nuts for small stuff up to 4mm cable.
 
4mm diameter is 12.5sq mm
Take a bit off for the thread groove and it is pretty close to 10sq mm
 
Yes, but usually steel so closer to 1.2mm^2 copper in terms of conductivity. Less if stainless...
Over a distance of 1to 2 mm, I can’t believe the material resistance makes that much difference.
And often the screws are nickel plated brass.
 
In this case its just for earthing the armour which is not used as the cpc. But the earthing of the armour is required to be able to handle the full fault current and although I'm sure 6mm would be fine a lot of the time if table 54.7 is used (rather than doing the adiabatic calculation) then the fly lead should be the same size as the line conductor so 10mm is the requirement here. I can't think that this is so unusual so I'm surprised that 10mm lugs with small (M4) holes are not widely available.

Are you connecting to the armour at both ends of the cable? If you are then that will be 2x6mm in parallel.

Why not just get a plain lug and drill your own 4mm hole in it?
Lugs are available with pre-made holes in the commonly used sizes, plain lugs exist to fill in the gaps for the other sizes.
 
Well an M4 screw itself can't carry much current compared to 10mm cable, nor can it apply a lot of clamping force to make sure something that stiff stays in place, etc.

The screw shouldn't be expected current, it should only be clamping the lug to the brass.

Likewise the terminal screw shouldn't be making sure something stiff stays in place, the regulations require that terminations are not placed under any undue stress. Conductors should be formed (and supported if required) such that the termination isn't under stress.
 
Why? I use earthing nuts for all sizes of SWA gland and haven't had an issue.
They are a lot better in the 32mm and upwards sizes as they have an M8 stud instead of the little screws.

I'd only seen them up to 32mm as that's the largest I'd ever sourced. Recently I learned they're available up to 75mm and that their price is suitably frightening. Then again 300mm 4 core isn't exactly cheap, so cost pales somewhat in that regard.
 

Reply to What crimp for 10mm fly lead to earthing nut ? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
892
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
448
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock