Discuss 3 phase cable lengths in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Hello

Im confused, thats not hard though. Working in France(dont read too much into that), they give specific guidelines to follow so you dont have to do cable calcs and can just follow the tables. However theres something im not happy about. In their guidelines for cable lengths(to allow for a 2% VD) for a 36KVA 3 phase system they say for a 16mm² cable the max run you can have is 52m per phase. But for a 12KVA single phase system with 16mm² cable its only 27m.
Can anyone explain to me or at least point me in the right direction so I can figure it out as to why this is please? Because as far as I can see you allowed a maximum of 51.9A per phase with the 36KVA 3 phase system and 52.2A on the single phase system. Very similar. So how can nearly twice the cable length be allowed?
By the way I dont have any of my books out here and cant check this is out yet.
Thanks and I await your beratings
 
Hello

Im confused, thats not hard though. Working in France(dont read too much into that), they give specific guidelines to follow so you dont have to do cable calcs and can just follow the tables. However theres something im not happy about. In their guidelines for cable lengths(to allow for a 2% VD) for a 36KVA 3 phase system they say for a 16mm² cable the max run you can have is 52m per phase. But for a 12KVA single phase system with 16mm² cable its only 27m.
Can anyone explain to me or at least point me in the right direction so I can figure it out as to why this is please? Because as far as I can see you allowed a maximum of 51.9A per phase with the 36KVA 3 phase system and 52.2A on the single phase system. Very similar. So how can nearly twice the cable length be allowed?
By the way I dont have any of my books out here and cant check this is out yet.
Thanks and I await your beratings
ohms law mate, you will get it if you think
 
Thanks guys, its been 12years since ive had to do calcs and wow ive forgotten alot. Loving getting back into the theory side of it again. Its a good forum this, thanks for guidance!
 

Reply to 3 phase cable lengths in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock