Currently reading:
3 phase Zs test!!!!

Discuss 3 phase Zs test!!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

E

eskimo39

Hi guys does anyone know if is possible to do a 3 phase Zs test on a fluke 1653b? I am currently halfway through s PIR at a factory and most boards I have tested have either being single phase or 3 phase with no RCD. However I have 2 outside motor/ pump sockets to test but neither have a neutral and both are on RCD. I have tried combining my earth and neutral wires but it still trips. Any ids?
 
measure R1 +R2 on each phase. use highest reading and calculate Zs. ( R1+R2+Ze)
 
If the equipment can be shut down and you or the customer have spare mcb's, remove the rcbo from circuit and replace with a spare mcb to do the test (provided your meter will do a 2 lead impeadance test).(this method introduces extra risk to you in altering circuit make up and should be considered carefully)

If the rcd is not an rcbo and seperate from the DB, bypass it/link it out and carry out the two lead impeadance test. (less risk to your self and the norm)

If your meter does not carry out 2 lead impeadance tests the option would be as telectrix's post. (the safest and most sensible option)
 
Live testing (but particularly in an industrial installation) contravenes EAWR. If you require Zs this MUST be achived in the safest way possible, therefore R1+R2 dead + Ze Live but Installation dead. Only if isolation cannot be achieved or the test can only be done live (eg RCD test) is live testing of the installation valid under EAWR.
 
Live testing (but particularly in an industrial installation) contravenes EAWR. If you require Zs this MUST be achived in the safest way possible, therefore R1+R2 dead + Ze Live but Installation dead. Only if isolation cannot be achieved or the test can only be done live (eg RCD test) is live testing of the installation valid under EAWR.

What a load of old horsedung in the real world if a spark can't safely carry out a Zs test live then they shouldn't be doing it. I'd like to see you use that method when you have 100 plus circuits to check. Anyway you say R1+R2+Ze how the hell can you justify taking Ze if you are contravening EAWR. Anyway what's wrong with doing it the easy way and taking 3 tests, each phase to cpc and recording the highest?
 
What a load of old horsedung in the real world if a spark can't safely carry out a Zs test live then they shouldn't be doing it. I'd like to see you use that method when you have 100 plus circuits to check. Anyway you say R1+R2+Ze how the hell can you justify taking Ze if you are contravening EAWR. Anyway what's wrong with doing it the easy way and taking 3 tests, each phase to cpc and recording the highest?
his problem is that he can't carry out a Hi current Zs as the circuit is RCD. he can't carry out a no trip test as he hasn't got a neutral.
 

Reply to 3 phase Zs test!!!! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock