Search the forum,

Discuss 32amp socket connection for temporary cabin in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Can anybody help please.....I need to connect a cabin electrics to the house, appreciate normally long term this would be via fuse board direct, however I just wish to connect to the house using 13amp plug. The minimum draw from the cabin is 20amps, if I used a split socket 32amp to twin 13amp sockets and plugged into two house sockets would this work? Or any alternative suggestions? appreciate any help for this to effect a solution rather than direct to the main fuse board.....don’t wish to use generator if at all possible..thanks
 
Absolutely NOT

The splitter you are referring to is commonly referred to as a widow maker.

This needs connecting properly and rcd protected.
If this is a domestic property it will also need notification to building control unless a part p installer is used.
 
Absolutely NOT

The splitter you are referring to is commonly referred to as a widow maker.

This needs connecting properly and rcd protected.
If this is a domestic property it will also need notification to building control unless a part p installer is used.
Was suspecting this would be the answer...thanks for advice ...need a plan B...Thanks again...
 

Reply to 32amp socket connection for temporary cabin in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
886
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock