Discuss Can i wire an outside socket to a junction box located for a car charger? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin and eath cable and what looks like a Cat5 cable. The twin and earth is currently in connector blocks. This cable runs from the junction box straight to my Hager fuse board and is on a 32amp breaker. It is listed at the box as Car Charger which i imagine is done in case we want to add a car charger in the future. I want to remove the junction box and add an outdoor IP66 double socket but ideally would like to use the exisiting cable (6mm twin and earth) and the exisiting breaker (32amp) is this safely possible as i know both are higher than required. From what i have seen outdoor double sockets are normally wired in 2.5mm twin and earth and have an 13amp breaker?
 
It would be advised to get a spark in to down grade the fuse to a 16 amp in the Cu board and give you a minor test cert,
He can use the 6mm cable with out down grading that.
There's no benefit to downrating the circuit protection if there's a 6mm^2 cable there. That said, I'm not a fan of an EVSE being connected to a 32A protective device rather than a 40A as otherwise it's running at the full rating of the protective device for potentially many hours at a time.
 
The OP is only fitting a double socket to it.. It's not going to be pulling more than 32A
 
The OP is only fitting a double socket to it.. It's not going to be pulling more than 32A
Granted. My comment relates to how it was installed for the intended use. As such I don't believe that 32A was the correct choice. It is, however, ideal for a socket circuit.
 
It is in the main consumer unit
Ok... Its not a problem, but as others have mentioned, A 32A breaker would be running at its limit while charging....

You're not using the circuit for car charging, so not really a valid point.


A double socket, although possible to plug in 2 x 13A loads, may only be rated for 20A, so I would advise having the breaker size reduced to 16A, just to protect the socket. (Will never reach that value if only xmas lights)
 
A double socket, although possible to plug in 2 x 13A loads, may only be rated for 20A, so I would advise having the breaker size reduced to 16A, just to protect the socket. (Will never reach that value if only xmas lights)

Ok, I don't want to come across like some sort of grumpy old fart.. (which I am) and maybe I need to listed to Marie Carry sing "All I want for christmas is you" 20 more times, while headbutting a wall but....
I know where you are coming from, for safety reasons, but as most sockets are wired back to 32A breakers I don't really see the need and expense in changing the breaker.
 
if you were designing a circuit from scratch, knowing it was just going to be one outside socket (or two, being a double) then you wouldnt put it on a 32A.
Youde be protecting the cable.... which isnt an issue here, as its oversized anyway... ah... wait a minute......



Ok, scratch that. Im now thinking along the lines of an originally designed 32A radial wired in 4mm with regular double sockets on it. You could have the same 26A load plugged into any of them.

Ok. Just leave the 32A in place. Its not an issue.

"Grumpy old fart"?..... No, i think that particular scouser is laid up at the moment :)
 

Reply to Can i wire an outside socket to a junction box located for a car charger? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
999
Is this ok? 32amp breaker with a 6mm wire leading to fused cooker switch. This then leads with 6mm cable to hardwire point. Can i hardwire 2 x...
Replies
11
Views
736
OLDBOY
O
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
724
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
879
I collect old Electrical Fittings and I recently acquired this vintage Junction Box (photos attached). I've been trying to figure out how it would...
Replies
4
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock