Search the forum,

Discuss 400 amp bs88 in the UK Electrical Forum area at ElectriciansForums.net

ganzo

-
Reaction score
0
Hi

We have a LV section board supplied with 630mm singles. The ammeter on the board is reading 530 amps per phase. We checked upstream and it is supplied from 3x400amp bs88 fuses. Can anyone explain why the fuses can take this load without blowing. If so where can I get some documentation to back this up.

Thanks
 
You need the time/current curve for a 400amp bs88-2 at 530amps it will be unlikely to blow the fuses straight away but after a good duration ... I doubt this is a average demand you measured or they would have been taken out by now.


I will assume you have a calibrated clamp meter.

Check the max Kwh demand on the meter by cycling the button most let you do this...

How exactly are you measuring this value?
 
What is the max that a 400amp fuse could cope with?

Your not reading my replies as this is a overload their isn't a max you can apply you look at the current/time curve for the fuse and it will give you how long in seconds the fuse will hold for if that current is maintained.

If you are correct and this current was maintained the fuses will operate - what is the average value on your meter and again with what and how are you measuring it, and are you doing it correctly. I ask because like most you fail to fill your profile in so we have to ask you in simple terms as we can't guess your experience and qualifications.
 
The load is fluctuating as its a waste transfer site with lots of motors. There is a lcd display on the main incoming section where you can select kw amps or volts. I say 530 amps average per phase as the display is changing constantly.
 
Your seeing load spiking as the big motors this is especially common with shredding machines etc, the overcurrent last for a few seconds only before dropping back down.

You may want to review the sites KVA demand and your KVA allowance and see if you need to take measures... as you have ask this question to start with and seeing your confused with what your seeing and how to relate it to a time/curve chart then you may need to get an experienced person in to see if measures need to be taken before you end up with a power outage.

Have you any electrical background or you asking from a curious point of view with no training in this field?

If the DNO meter has buttons for cycling reading what does the max demand say in KVA or KwH?
 
You have got to log the usage over a shift at least.

I’m surprised the DNO has allowed consistent overload for any length of time. We were penalised if we overstepped the mark.
 
Thanks for the advice guys. Not in work at the moment but will have a another look tomorrow and hopefully get more details. That's if the lights are on.
 

Reply to 400 amp bs88 in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock