a live from each side. A neutral plus earth
No neutral - the two lines of the split-phase supply are a 460V single-phase supply as far as the VFD is concerned. Obviously they must both be fused and switched as lines, rather than a line and a neutral.
 
No neutral - the two lines of the split-phase supply are a 460V single-phase supply as far as the VFD is concerned. Obviously they must both be fused and switched as lines, rather than a line and a neutral.
Understood, can probably just take a line from each 240v consumer unit then. Don't you need a neutral with these vfds then?
 
can probably just take a line from each 240v consumer unit then

Nope, that could backfeed one CU from the other when switched off, a very dangerous situation. Any switches / MCBs anywhere on the 460V circuit from suppliers' meter to VFD must be linked double pole devices. IIRC not all 3-phase boards are officially rated for 460V, worth checking.
 
Nope, that could backfeed one CU from the other when switched off, a very dangerous situation. Any switches / MCBs anywhere on the 460V circuit from suppliers' meter to VFD must be linked double pole devices. IIRC not all 3-phase boards are officially rated for 460V, worth checking.
Maybe a stand alone double pole switch mounted in an enclosure would be the way to go, what about the neutral though? Not required?
 
Not for the VFD power itself. If the machine had any auxiliary devices, lights etc. they might need the neutral (or need feeding separately from a 230V circuit).
 

Reply to 480v Split Phase, new workshop, VFD's required in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock