Currently reading:
4mm/2.5mm T&E

Discuss 4mm/2.5mm T&E in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
44
Hi all, looking to potentially wire some new sockets in a 4mm radial rather than 2.5mm RFC. Been my preference for ages, find it less hassle to install, and 25A is plenty.

That being said, something I've always been a bit tetchy over is the potential worst case touch voltage given the "normal" 1.5mm CPC. I'd feel much happier, and prepared to spend the bit extra to get 4mm/2.5mm T&E to bring that figure down a bit. I'm sure this used to be readily available years ago from the usual wholesalers, but these days I can't see it anywhere.

Am I going mad, or is this stuff impossible to find these days?
 
Hi all, looking to potentially wire some new sockets in a 4mm radial rather than 2.5mm RFC. Been my preference for ages, find it less hassle to install, and 25A is plenty.

That being said, something I've always been a bit tetchy over is the potential worst case touch voltage given the "normal" 1.5mm CPC. I'd feel much happier, and prepared to spend the bit extra to get 4mm/2.5mm T&E to bring that figure down a bit. I'm sure this used to be readily available years ago from the usual wholesalers, but these days I can't see it anywhere.

Am I going mad, or is this stuff impossible to find these days?
I have never come across 4mm/2.5mm. Even when I have come across very old 4mm (eg copperclad from early 70's), it had a 1.5mm CPC.
 
Maybe runs through insulation.
not in a kitchen. overload would be a problem.
Both of these in reality. Needs to run through insulation, and it's heading to a (light use) workshop where 20A could cause load issues. Could just run a 2.5mm RFC, that's just... well, not my first preference shall we say, without getting into the ring vs. radial bloodshed!

I'd be happy to send you a few rolls, postage might be a bit much though. :)
Thanks for the offer but yeah, wouldn't be too keen to pay the postage on that lot! I'm curious as to where you get that from though? Think I got some from TLC last time, but that was a long time ago. Might have even been in old colours.

I'll probably just use the standard 4/1.5 stuff, was just wondering if there was an obvious place I was missing.
 
Thanks for the offer but yeah, wouldn't be too keen to pay the postage on that lot! I'm curious as to where you get that from though?
Anywhere really, the standard in Oz is for 2.5-6mm2 twin and earth to have a 2.5mm2 earth conductor. Probably related to the fact that we use C-curve MCBs as our standard breakers, quite uncommon to see a B32 here.
 
Anywhere really, the standard in Oz is for 2.5-6mm2 twin and earth to have a 2.5mm2 earth conductor. Probably related to the fact that we use C-curve MCBs as our standard breakers, quite uncommon to see a B32 here.
Ah, interesting, the things you learn. Had no idea C curve was standard there!
What about buying from Ireland, I believe they now have full size insulated earths in their T&E.
I'm not sure I'd even go to those lengths really, though my understanding is that 4mm is basically unheard of over there anyway.
 
Agree with the 4mm radial argument but what happens a year down the line when they want an additional spur from a socket...3 x 4mm cables in a socket, a bit tight or not?

Not sure about other brands, but all the normal MK sockets I've seen are rated for 3x4mm (search for "terminal capacity" in this doc: https://www.mkelectric.com/Document...Dimensions tech pages for catalogue FINAL.pdf)

In any case, that's actually an advantage in my book - you can branch from a radial all day long without too much consideration, whereas the number of times I've seen cowboy style ring spurs (6 double sockets hanging off a single unfused spur, plus sometimes broken the ring in the process) makes me uneasy.
 
To avoid sending this thread off at a tangent….

 

Reply to 4mm/2.5mm T&E in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top