Discuss Outside socket spurred from the ring main. query! (I am a long Serving electrician) in the UK Electrical Forum area at ElectriciansForums.net

michaelw6

-
Arms
Reaction score
27
Ok i may get slated for this one but here goes; A bit of background info first.
Its been a while since ive looked at my iee regs, and ive not done my 18th edition but get the updates. i no longer practice much electrical due to a career change.
But for friends, family old customers when i get time i still do the odd little job.
I have been asked to install an outside socket which normally is never an issue just to spur of an internal socket.
This time ive been asked to install a socket 6m away for one of those inflatable hot tubs.
As i remember the regs state you can spur off a socket in 2.5mm t&e im sorry but i dont recall it ever mentioning lengths.
Now a 2.5mm twin and earth is only capable of 25A approx if you plug in two 13A sockets thats 26A. That all works but are we forgetting its on a 32A MCB that cable would burn out before the mcb trips if there was an overheating issue?
Im pretty sure the 6m is not that much of an issue. but if i do a cable calc for this little job it says the cable should be 4mm, im assuming due to the 32a mcb.
Im contemplating installing a XLPE SWA 2.5mm² 6943X 3 core to a single socket, the cable being rated at 31A and a single socket at 13A.?
So putting all the questions to one side and working on the above assumptions.
Would you install a 2.5mm or 1.5mm armoured or a 4mm?
To either a single or double socket?
to be safe than sorry and to future proof i could just install a 4mm to a double socket!!
 
Ok i may get slated for this one but here goes; A bit of background info first.
Its been a while since ive looked at my iee regs, and ive not done my 18th edition but get the updates. i no longer practice much electrical due to a career change.
But for friends, family old customers when i get time i still do the odd little job.
I have been asked to install an outside socket which normally is never an issue just to spur of an internal socket.
This time ive been asked to install a socket 6m away for one of those inflatable hot tubs.
As i remember the regs state you can spur off a socket in 2.5mm t&e im sorry but i dont recall it ever mentioning lengths.
Now a 2.5mm twin and earth is only capable of 25A approx if you plug in two 13A sockets thats 26A. That all works but are we forgetting its on a 32A MCB that cable would burn out before the mcb trips if there was an overheating issue?
Im pretty sure the 6m is not that much of an issue. but if i do a cable calc for this little job it says the cable should be 4mm, im assuming due to the 32a mcb.
Im contemplating installing a XLPE SWA 2.5mm² 6943X 3 core to a single socket, the cable being rated at 31A and a single socket at 13A.?
So putting all the questions to one side and working on the above assumptions.
Would you install a 2.5mm or 1.5mm armoured or a 4mm?
To either a single or double socket?
to be safe than sorry and to future proof i could just install a 4mm to a double socket!!

I don't understand reasoning behind the difference in taking your feed from a single or a double socket?

The distance will obviously affect the volt drop, but as you say it's not a particularly great length.

What current is required by this hot tub?
 
I don't understand reasoning behind the difference in taking your feed from a single or a double socket?
I may be wrong but I think he means fitting a single or double socket to the end of the spur not at the feed.
 
I may be wrong but I think he means fitting a single or double socket to the end of the spur not at the feed.

Ah yes. I've just read it again and I think I misunderstood.
 
It’s standard to think of a double socket as taking only 20A between the two outlets, not 26…. 2 x 13A

Spurring off a rfc with 2.5 to a double socket is permitted, whether it’s 6m away or only 6 inches.


An inflatable hot tub may only be rated at 10A anyway….


For risk of overloading, I’d avoid taking a socket for a hot tub off the same circuit as washing machines, dishwashers, tumble dryer etc.
 
A double socket is permitted in a 2.5mm spur from a 32a ring main due to secondary protection (26 amps - 2x 13amp plugs is the maximum load that 2.5mm will see).

Secondary protection allows a whole load of things that most guys wouldn’t do. An example - a 1.5mm fed from a cooker outlet (32amp) to fed a cooker hood - as long as the hood is fed via a fuse spur or single socket there’s nothing wrong with it.
 
hot tub about 11Amps.
So in theory if its just a double socket i could get away with 2.5mm 3c armoured. no FCU. and yes it has RCD of course!
Its coming off the kitchen ring as its the only nearest power supply.
i will put a single socket on it though as i dont like the idea of them plugging something else in like a 2kw heater as well as the hot tub.
 
While no need to feed of a FCU in only one single/double socket, there is an argument for having some means to switch it off if faulty so rest of RFC can be kept on. Any DP switching FCU would achieve that as well as allowing a double socket and no worries of stupid levels of current being drawn.

If cabled in SWA and done by someone like yourself then a fault is unlikely, but future damage might see water in outdoor socket tripping RCD, etc.
 
While no need to feed of a FCU in only one single/double socket, there is an argument for having some means to switch it off if faulty so rest of RFC can be kept on. Any DP switching FCU would achieve that as well as allowing a double socket and no worries of stupid levels of current being drawn.

If cabled in SWA and done by someone like yourself then a fault is unlikely, but future damage might see water in outdoor socket tripping RCD, etc.
I did contemplate a FCU, and thought about the isolation issue. But that only lasted a second!!! LOL
No honestly a FCU would be an idea rather than a wiska box on the back to back of the socket.
 

Reply to Outside socket spurred from the ring main. query! (I am a long Serving electrician) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
200
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
743
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
861
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock