now you are trolling, ridiculousAlso, I'm a little uncomfortable, given the number of radio ads about overloading four way bars are fires. Not least since the install is the reinstatement after a fire
Discuss 5 kitchen sockets from 1 FSU in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
now you are trolling, ridiculousAlso, I'm a little uncomfortable, given the number of radio ads about overloading four way bars are fires. Not least since the install is the reinstatement after a fire
Post #6 Trev, an afterthought after 3 months.The guy came up with this arrangement on a rewire? Crikey!
Well spotted DaveyPost #6 Trev, an afterthought after 3 months.
433.1.1 said:Every circuit shall be designed so that a small overload of long duration is unlikely to occur
433.1.1(i) said:The rated current or current setting of the protective device (I[SUB]n[/SUB]) is not less than the design current (I[SUB]b[/SUB]) of the circuit
I will be honest, I have done the exact same thing for a client. For two double sockets supplying kettle, toaster, radio and a spare. So not as potentially heavily loaded as the OP. I explained the limitations and possible issues that may arise. I also explained the correct way it should be wired. The client did not want to renew tiling etc so this was pretty much the only option remaining.
To date they have not had to replace the FCU fuse that I know of. I do not feel it breaches 433.1.1 as any overload would be for a short period of time, not a "long duration".
What do others think is the best option: down rating cct to 20A or doing as has been done in the OP, given that redecoration is a no-no (is'nt it fickling always!!!)??
I think it's unfair to compare your situation with that of the OP, you clearly wanted to install a ring, but the client, whose decision it is, did not want the problems and costs involved, so you completed the job in the only practical way you were able whilst still complying with the Regs and you took the time to explain the situation to the client, who clearly understood. The OP is implying the decision was made by the installer because it was convenient to them and no other factors were taken into account, so whilst the circuit is generally compliant i think we could all consider this a case, "Just because you can, does not mean you should"
Though must say customers can be prone to lying occasionally!!
If the OP was not consulted about changing spurs to a ring then the spark is defo in the wrong.
I think it's unfair to compare your situation with that of the OP, you clearly wanted to install a ring, but the client, whose decision it is, did not want the problems and costs involved, so you completed the job in the only practical way you were able whilst still complying with the Regs and you took the time to explain the situation to the client, who clearly understood. The OP is implying the decision was made by the installer because it was convenient to them and no other factors were taken into account, so whilst the circuit is generally compliant i think we could all consider this a case, "Just because you can, does not mean you should"
Excuse my limitation to O level english but did that sentence make sense? I comprehend 433.1.1 just not the "thus allowing short ... duration low level overloads IS a breach of the Regulations 433.1.1"It could be argued that considering the location of the circuit it is a reasonable conclusion that the load on the circuit, even for short duration, may exceed 13A and as such just assuming the fuse will protect the circuit, thus allowing short or even extended duration low level overloads IS a breach of the Regulations as required by 433.1.1 Every circuit shall be designed so that a small overload of long duration is unlikely to occur