Customer has himself fitted a new hob of 6.4kw in place of previous gas hob with electric ring x 1 ?
Under the hob there was x 2 sfcu both on there own circuits and both run in 1 x 2.5mm t/e.
He has connected his hob to one of the sfcu fused at 13a and on a 16a MCB at the board.

Using diversity this should do.
However, could he connect both runs of 2.5mm (in theory then 5mm) to a new cooker connection plate and place on 32a mcb covering the max 26.7a of the Hob.
Or is that a No No.
 
as long as the 2 cables are of equal length ( resistance) and follow the same route, then it's parallel conductors and should be OK. however, a 6mm cable with a cooker isolator and dual outlet pl,ate would be more conventional.
 
Somebody asked this same question a few weeks ago, but for installing a shower rather than a cooker. Might be worth searching for it, as there were many replies.
 

Reply to 6.4kw hob circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock