Discuss Switching and isolation for cooker and hob on same circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Evening all,

I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the kitchen ring. My thoughts are that with diversity and the fact both the oven and hob are on 13amp plugs or rated at less than that, then they could go on a 6mm2 dedicated combined circuit

As the appliances need to be fused down to 13A I'm wondering what people thoughts are on switches and isolation for each...I ve seen double appliance outlets which could be fed from a singular outlet but these wouldn't be fused


Look forward to any responses

Thanks
 
What is the rating of the induction hob?

What is the rating of the induction hob?
Sorry for slow reply...I'm not 100% set on anything yet...I think the oven would be 2300 ish and 7350 for the hobs or less...meaning would need a 40a after diversity for the two

So I thought probably go with a 6mm that I've installed to a 45 amp switch then to a dual appliance outlet then one straight to the hob and one to a spur supplying the oven
 
Note 4 above… we don’t have GFCI’s in the Uk.
We call them RCD, or RCBO (residual current device/ residual current breaker operated)

Both generally do the same job

And in Uk, the use of these devices have increased due to the final use of the circuit, and the way it has been run in.
 
On the OP, you said both hob and oven were on a 13A plug…

Now the hob is 40A??
Sorry I'm not 100 % on which units I'll end up and after reading a few ratings online they seem generally a larger load...Still a 40a circuit with 6mm2 cable seems to suffice and i can utilise one 45a switch to a dual outlet plate....the issues comes after this point if a oven requires fusing to 13A
 

Reply to Switching and isolation for cooker and hob on same circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
647
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock