Jeffmo65

Hi Guys ?
We have been asked to install some additional bits of kit to a small supermarket . Everything is metered ie; lighting , general power refrigeration and so on . We have been told by the consultant that they have an ASC of 60 KVA . I visited site the other day to carry out some investigation . On clamping the singles , I found that
L1 = 128amp
L2 = 92 amp
L3 = 112 amp
Fitted are 200 amp fused main switch .
Now they are also saying they are max ASC Of 57.5 KVA according to their metering analysis .
Doing some 3 phase maths , their statement that they are 2.5 % under agreed ASC doesn't run true as I have them over already . Any thoughts chaps
 
but how constant are your readings? they could be a peak loading.
 
but how constant are your readings? they could be a peak loading.
I appreciate your comment . My clamp meter was left on for approximately 2 hrs . Checking at 20 minute intervals , it did not seem to deviate much . There peak reading analysis was
L1= 158.1
L2= 120.2
L3= 154.9
To be honest this just does not equate to me . Perhaps I am doubting myself too much ?
 
So they are exceeding their ASC (authorised supply capacity) get in touch with DNO and get an upgrade. This may be as simple as a new connection agreement or involve some major network reinforcement.
 
I’ve come across a beauty with this. A company paying for an ASC that the supply couldn’t possibly match. A new substation is now to be installed.

I’ll keep quiet other than the above as this involves another forum member.
 
The only way to prove (or otherwise) your concerns is to hire a power analyser and leave it connected to cover at least a week's typical trading days.

Our forum sponsor (test-meter) hires such equipment out. It'll be proof positive one way or the other together with results being downloadable to a computer or printed out in hard copy form!!
 
To be honest I have obviously seen analysers been used but have never physically connected or used one . So excuse my ignorance in this matter , how complicated are they to read / connect . Apart from being able to interpret the results would I require any additional skills ? .
 
The ones I use have three rogowski coils for measuring the current and leads for each phase voltage and neutral. You will need the software to download and read the results.
Basic results will be the max, min and average current and voltage. More advanced are harmonic distortion and flicker short and long time.
 
To be honest I have obviously seen analysers been used but have never physically connected or used one . So excuse my ignorance in this matter , how complicated are they to read / connect . Apart from being able to interpret the results would I require any additional skills ? .

They are a doddle to set up and comes with all the software to download to your computer, depending on the units storage memory, and the number of parameter values you choose to record, you can take readings anywhere from every second to every hour or more.

You can always get full information from test-meter, along with recommendations as to what unit best suits your needs!!
 

Reply to Additional equipment . Total ASC required in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock