Hi

I am looking at purchasing and running a drinks cooling machine to run on no mains electric what so ever!



The company that sells the machine have advised the following

Frequency: 50Hz Rated current: 5.5A Rated input: 800W



This machine is a liquid to liquid based (water and anti freeze bath) heat exchange and only runs when liquid is passing though it. And will only operate when I open the tap and fill a glass up from it so it will not be running most of the time



The two option I am considering is buying a generator inverter and battery and charging the battery up as required. Or just running the generator when it is in operation. So what do you think?



Thanks
 
Looking after a generator is a pain, but presumably you don't have the options for that much power otherwise.

If it is a drinks machine you probably want as little noise as possible, so look for that in any specification as it might pay for a slightly bigger model that has a better silencer, etc.

Leaving generators running on no/light load is not good for them, especially diesel type (search for "wet stacking") so if you have the budget, space and transport (if necessary) then running a generator for short periods at high load to charge a large car/lorry/boat battery and then running your kit off an inverter from that might be better overall, even if the initial cost is a bit higher.
 
Does this use compressor refrigeration? Your description suggests not, but if it does, allow for a compressor starting load of 3-5 times the running load. This is quite critical especially if it is designed to start against remaining head pressure. With an undersized generator or inverter if the compressor stalls and trips its thermal protection, it might not then be able to restart for a further 5 minutes. Also, if the load on a small generator is mostly from an induction motor, a self-regulating alternator will tend to drop out of voltage regulation due to the low power factor. An inverter generator or one with a proper AVR is beneficial.

Can you post or link to the machine specs?
 
yes it is
OK, I thought as much. Be aware that for a variety of reasons most event sites expressly forbid 'private' generators and insist that if you need power then it's provided by the event electricians (aka 'hook-up'). So before you spend anything I'd strongly suggest doing your homework on that aspect first. I say this as an experienced events electrician!
 
Hi

I am looking at purchasing and running a drinks cooling machine to run on no mains electric what so ever!



The company that sells the machine have advised the following

Frequency: 50Hz Rated current: 5.5A Rated input: 800W



This machine is a liquid to liquid based (water and anti freeze bath) heat exchange and only runs when liquid is passing though it. And will only operate when I open the tap and fill a glass up from it so it will not be running most of the time



The two option I am considering is buying a generator inverter and battery and charging the battery up as required. Or just running the generator when it is in operation. So what do you think?



Thanks
May I ask you to amplify what ‘drinks’ you want to ‘cool’? What form do the drinks have before the need to cool? Could you also say something about a typical day’s business selling these cooled drinks: How many in total? What volumetric quantity is each drink? What rate of sale? How many days per week, per month, per year?

and do want to keep already cool drinks cool or to cool drinks which presale are at ambient temperature?
 
Last edited:
OK, I thought as much. Be aware that for a variety of reasons most event sites expressly forbid 'private' generators and insist that if you need power then it's provided by the event electricians (aka 'hook-up'). So before you spend anything I'd strongly suggest doing your homework on that aspect first. I say this as an experienced events electrician!
sorry there is no chance of mains, but I will need a fairly silent generator like a Honda due to noise to local residents
 
May I ask you to amplify what ‘drinks’ you want to ‘cool’? What form do the drinks have before the need to cool? Could you also say something about a typical day’s business selling these cooled drinks: How many in total? What volumetric quantity is each drink? What rate of sale? How many days per week, per month, per year?

and do want to keep already cool drinks cool or to cool drinks which presale are at ambient temperature?
They are 11 kegs of beer that a forced out of the keg (at room temrature) by C02 and into the drinks cooler

To be used all weekend
 
Hi,i have done a similar project for a pal,and on assessment,we worked out the following....

You will not want a geny running full time,for sporadic use,and you will not want to start a geny,string or buttton,on every need...

Add to that the extra issues of fuel,security and reliability,and we plumbed for bank of 4 deep cycle batteries paralleled up to an inverter.

These were mounted in a cradle underneath the trailer,and charged up at base,and i believe we had to over spec the inverter,but it worked ok.

You may need to find out some details regarding the start current,running load,and cycle pattern of your chiller,in order to plan an accurate choice of useable stored power,remembering minimum voltage requirements,standby losses,etc.


Just to cheer you up,if you opt for a small,quiet generator,in the scenario described,get two....

If you don't have theft or a breakdown in the first dozen outings....it'll be a first?
 
Hi,i have done a similar project for a pal,and on assessment,we worked out the following....

You will not want a geny running full time,for sporadic use,and you will not want to start a geny,string or buttton,on every need...

Add to that the extra issues of fuel,security and reliability,and we plumbed for bank of 4 deep cycle batteries paralleled up to an inverter.
Where you running a drinks chiller? What kind of drinks where you doing?
Can you recomend any batteries; As they all very in size. What size inverter did you have?
Thanks
 
I designed a system to power 20 odd catering vans, each with chest freezer, 2 tall larder fridges, lighting and payment system using solar power Mar-Oct - and on peak solar days in summer a 1kW hand hot water heater. Other times a Honda engined 3.4kVA LPG generator with automatic voltage regulator provides van power during opening hours and charges the batteries for overnight use.

This is the robust 3kW inverter which has a very high peak power capability (9kW), pure sinewave and 'sleep' mode when load drops below 75W and wake up when load rises above this figure which conserves battery power.

12V solar panels charging kits for caravans, motorhomes, boats, yachts, marine - https://www.photonicuniverse.com/en/catalog/full/164-3000W-24V-low-frequency-pure-sine-wave-off-grid-inverter-peak-power-9000W.html

Batteries are Advanced Gel Matrix by Victron:

12V solar panels charging kits for caravans, motorhomes, boats, yachts, marine - https://www.photonicuniverse.com/en/catalog/full/470-200Ah-12V-Gel-deep-cycle-battery-for-motorhomes-caravans-boats-and-off-grid-power-systems.html

Either 6 x 200Ah or 4 x 300Ah, wired in strings of 2 batteries in series to give 24V and these then connected in parallel. The theoretical power available from fully charged to batteries 'flat' is 12 x 1200 = 14.4kWh but this is not achieved nor relied upon. Instead the batteries are never discharged more than 50% to preserve their life; thus about 7kWh is the working amount of electrical energy available.

7kWh would run an 800W cooler constantly for 7000/800 = about 9 hours.

This system is static apart from when the catering van is driven to and from site for its annual maintenance and refurbishment - the electrical wiring and electronics is only shaken about for a few hours each year. Of 20 vans we have only had one inverter failure which was on arrival not when in use and the supplier replaced it.

Don't operate at 12V. Use 24V and the cabling must be multi-stranded with properly crimped on ring terminals tightly bolted. One needs to buy a hydraulic crimper tool.

The amount of energy stored in each battery and then as a bank is extraordinarily high and it is highly dangerous if a battery or the bank is short circuited or if there is a fault current. Circuit breakers are essential and the battery must be located in an lockable enclosure. Special precautions, insulated tools and personal protective equipment are required when connecting up the batteries and high current 24 V cabling: this is a job for a skilled person. I wrote a procedure to do this which is followed to the letter.

The flat roof of the catering vans has a 1.5kW array of solar voltaic panels to charge the batteries.

On the mains voltage side everything has to be done to meet the IET electrical installation regulations and my client (brother in law) has to have annual certificates for inspection and testing including PAT of the electrical items for him to operate. We include the 24V dc and the solar photovoltaic wiring in the inspection and testing since it too can kill or harm just as much as the 240V.

I will not say more because I do not want to design your working safe system. There are safety features and programming of the inverter to do for the intended application. I suggest you contact Tom at Photonics Universe for further advice and an electrician familiar with off-grid battery to mains installations. I strongly advise against doing it yourself because you are not competent and do not know how to deal with all the risks.

PS: I am not saying this set up will satisfy your requirement. I have not done the analysis which should include whether you would be wiser to just use a generator to meet the business and operational requirement as distinct from the technical requirement.
 
Last edited:
Just to add for the OP that "you are not competent" has a specific meaning in terms of electrical regulations. They divide people in to electrically skilled and competent (i.e. trained electricians and the like) who can be expected to work safely on electrical systems, and the rest of the population.

It has nothing to do with your competence in any other aspect of life!
 
I designed a system to power 20 odd catering vans, each with chest freezer, 2 tall larder fridges, lighting and payment system using solar power Mar-Oct - and on peak solar days in summer a 1kW hand hot water heater. Other times a Honda engined 3.4kVA LPG generator with automatic voltage regulator provides van power during opening hours and charges the batteries for overnight use.

This is the robust 3kW inverter which has a very high peak power capability (9kW), pure sinewave and 'sleep' mode when load drops below 75W and wake up when load rises above this figure which conserves battery power.

12V solar panels charging kits for caravans, motorhomes, boats, yachts, marine - https://www.photonicuniverse.com/en/catalog/full/164-3000W-24V-low-frequency-pure-sine-wave-off-grid-inverter-peak-power-9000W.html

Batteries are Advanced Gel Matrix by Victron:

12V solar panels charging kits for caravans, motorhomes, boats, yachts, marine - https://www.photonicuniverse.com/en/catalog/full/470-200Ah-12V-Gel-deep-cycle-battery-for-motorhomes-caravans-boats-and-off-grid-power-systems.html

Either 6 x 200Ah or 4 x 300Ah, wired in strings of 2 batteries in series to give 24V and these then connected in parallel. The theoretical power available from fully charged to batteries 'flat' is 12 x 1200 = 14.4kWh but this is not achieved nor relied upon. Instead the batteries are never discharged more than 50% to preserve their life; thus about 7kWh is the working amount of electrical energy available.

7kWh would run an 800W cooler constantly for 7000/800 = about 9 hours.
Did you use all of that set up to power all of the vans at once?
 
No, poor writing. Each van had an installation since the fleet of them is dispersed around England. I tried to persuade my client/BIL to use Honda inverter generators but he continued with the conventional Honda GX engined frame generators because he and his team knew them so well and had a maintenance and repair set-up for them already. It is the engine which fails not the alternator. My BIL changes engines and sets them up to start and run correctly.

Generators are attractive items to 'certain' folk and are easily stolen unless solidly chained to something immovable or built in to the structure. Overnight or when unattended, if not built in to the structure behind a very strong locked door (obviously when shut down) or if left chained up outside they will soon disappear.
 
The company that sells the machine have advised the following

Frequency: 50Hz Rated current: 5.5A Rated input: 800W


This is the robust 3kW inverter which has a very high peak power capability (9kW), pure sinewave and 'sleep' mode when load drops below 75W and wake up when load rises above this figure which conserves battery power.
Surly not in my case is it not?
 
Yes. If food is kept in a fridge or freezer to be sold to the general public then those fridges and freezers must always have electricity to maintain their correct temperature. It is not satisfactory to rely on their insulation. This applies to my clients business and is a condition of his licence to operate on the sites he trades at.

We tried electric-start Honda frame generators triggered to start by a separate thermostat inside the fridges and freezers but they did not start reliably and had to be exposed to the possibility of theft in order to run. The modifications to do this to the van were unacceptable we decided after doing one van.

When I did the analysis, it is more economic too because the generators consume less gas, break down less frequently and have a longer life. Two other benefits are the van is quieter more of the time and produces less CO2. The staff, mainly women, also like not having to start and stop and regularly checking the gennie.

As I finished with in one of my earlier posts I am not suggesting this is your solution but rather something similar and at a smaller scale. For example you said it only operates at the weekend whereas my solution is every hour, every day all year.
 
Last edited:
The first vans used a 2kW (6kW peak) inverter without problem. We upped the power to 3kW because we wanted to have the spare capacity to run other equipment which so far has not happened. The marginal increase in cost was small.

I have most likely taken you down a rabbit hole and your solution will be much simpler and cheaper. I did suggest you contact Tom and an electrician who does off-grid installations. Or you can just buy a generator after seeking advice on kVA from the supplier. It is difficult to advise you on kVA without knowing more about the beer cooler refrigeration system so we tend to say anywhere between 5-10 times the running power for generator kVA and buy one with an automatic voltage regulator AVR. It becomes a little more complicated if you have several motors supplied by the same generator but you indicate you only have one to start.
 
Last edited:
Surly you are not tell me each van had 6X £350 vorth of batteries and a £500 invertor to run a couple of houes hold fridges?
It really is a design aspect. You and whoever is doing the electrical design side have to work out what the load is:
  • Peak demand as fridge(s) kick in as that sets the inverter size)
  • Average between charging based on the insulation quality, throughput of drinks bring cooled, and any other loads (e.g. LED lights, payment system, etc) as that sets the battery size.
If you can charge from mains overnight then it might be worth spending more on batteries and not on a generator.

If you simply have to have a generator (e.g. parked in the middle of nowhere for days on end, etc) then you might decide on smaller and cheaper batteries and a charge pattern of running the genny a couple of times per day (ideally electronically controlled starting so staff don't need to worry about it). But then you have the issues of safe ventilation for CO poisoning risk, fire hazards if near dry long grass or similar, any permits/permission or restrictions for handling/storing fuel (near arable land, rivers, etc), the risk of theft, ongoing maintenance costs for the generator's engine, etc.
 
It really is a design aspect. You and whoever is doing the electrical design side have to work out what the load is:
  • Peak demand as fridge(s) kick in as that sets the inverter size)
  • Average between charging based on the insulation quality, throughput of drinks bring cooled, and any other loads (e.g. LED lights, payment system, etc) as that sets the battery size.
If you can charge from mains overnight then it might be worth spending more on batteries and not on a generator.

If you simply have to have a generator (e.g. parked in the middle of nowhere for days on end, etc) then you might decide on smaller and cheaper batteries and a charge pattern of running the genny a couple of times per day (ideally electronically controlled starting so staff don't need to worry about it). But then you have the issues of safe ventilation for CO poisoning risk, fire hazards if near dry long grass or similar, any permits/permission or restrictions for handling/storing fuel (near arable land, rivers, etc), the risk of theft, ongoing maintenance costs for the generator's engine, etc.
Nicely put.
 
Yes. If food is kept in a fridge or freezer to be sold to the general public then those fridges and freezers must always have electricity to maintain their correct temperature. It is not satisfactory to rely on their insulation. This applies to my clients business and is a condition of his licence to operate on the sites he trades at.
Did you or him ever consider consider cooling down with ice every day?



We tried electric-start Honda frame generators triggered to start by a separate thermostat inside the fridges and freezers but they did not start reliably and had to be exposed to the possibility of theft in order to run. The modifications to do this to the van were unacceptable we decided after doing one van.
When I did the analysis, it is more economic too because the generators consume less gas, break down less frequently and have a longer life. Two other benefits are the van is quieter more of the time and produces less CO2. The staff, mainly women, also like not having to start and stop and regularly checking the gennie.
So did you not bother with generators for the rest of the fleet in the end; where by you charged the batteries up from mains from a building?

I have most likely taken you down a rabbit hole and your solution will be much simpler and cheaper. I did suggest you contact Tom and an electrician who does off-grid installations. Or you can just buy a generator after seeking advice on kVA from the supplier. It is difficult to advise you on kVA without knowing more about the beer cooler refrigeration system so we tend to say anywhere between 5-10 times the running power for generator kVA and buy one with an automatic voltage regulator AVR. It becomes a little more complicated if you have several motors supplied by the same generator but you indicate you only have one to start.
I have looked online again for other beer chiller as I was not happy with the tecnical speck I was given for the chiller I was quoted for. Have a look at this one
BRW36H Series Water Cooled Range Base - https://www.booth-dispensers.co.uk/Catalogue/Products/Brewery-Equipment/Beer-Coolers/BRW36H-Series-Water-Cooled-Range-Base-2
Its about the closest I could find to my needs. there is the option on that page to download a manual but you have to email the company to get it (so have done so)

You said on this project for you customer you installed fridges for him. Are these domestic type fridges? The reason I ask is I was adviced not to use fridges as they do not oporate well when in transit. The gases need to settle first and can take up to 24hrs. I was also told that they only consume a lot of power when they start up from warm and cool the contence of the fridge down. But once cool they use very little power keeping them cool at all
 
Either 6 x 200Ah or 4 x 300Ah, wired in strings of 2 batteries in series to give 24V and these then connected in parallel. The theoretical power available from fully charged to batteries 'flat' is 12 x 1200 = 14.4kWh but this is not achieved nor relied upon. Instead the batteries are never discharged more than 50% to preserve their life; thus about 7kWh is the working amount of electrical energy available.
I was always on the idea that batteries should by fully charged and then fully discharged to flat and fully charge again to increase there life spam. Is this then wrong? or dose it depend on the type of battery?
Thanks
 
Taking your questions in order:

1. My client has 20 or so vans at 20 or so locations. He would have to build 20 ice making systems and then transport the ice blocks each day of the year. It is however a very good idea to keep the freezers filled up with frozen goods and if they cannot be done with produce then frozen blocks can fill in the gaps. He keeps his freezers over half full.

2. I was not clear enough. Each van still has a generator to cover the winter months and some prolonged periods during the year when sunshine alone is not enough to keep the the batteries sufficiently charged. The batteries must have by the end of working day enough power to maintain the refrigeration overnight and on some sites from close of play Saturday to opening up Monday morning. All his fridges and freezers have max and min thermometers inside them to check the food has been kept safely frozen or chilled. Before going on site the fridges and freezers are brought to the required temperatire either from solar of mains. It depends on the time of year they first arrive on site after refurbishment or from start up.

3. He was not allowed access to the site‘s power supply, not even from lamp standards nearby. He had to be completely off grid.

4. I repeat, in order for him to obtain a licence to operate and liability insurance The fridges and freezers have to have power available constantly for them to run as demanded by their thermostats. He previously operated using gennies running during the day and reliant upon the freezer or fridge insulation keeping contents cold enough when the van was closed for business. Alas, another licence holder, using the same scheme sold some burgers which had been defrosted while the gennie was shut down overnight in hot summer period and then refrozen when the genie was running again next day, and then cooked. the punter who ate them was very poorly afterwards.

5. I will read the product spec you provided tomorrow.

6. My client buys domestic fridges and they are changed for new every couple of years. He buys LEC and the ones capable of being placed in a warm environment - fridges and freezers have environmental classes to suit where they are used in the world. This should be taken into account also for one placed in a warm garage or conservatory.

7. Yes, one should allow some time for the gas to settle before powering up after significant motion of them. My client allows a few hours not 24 hours.

8. Yes, Fs and Fs need time and energy to cool their contents to the point that they are thermostatically regulated in temperature. Opening the door or lid of course will demand some energy during normal operation and placing products inside which need cooling. Every time the motor starts to run the compressor there is a brief surge in power/current drawn to quickly accelerate the mechanical components to running speed. When running the power/current is that necessary to run the refrigeration. Think about you having to quickly run up to speed a children’s roundabout and the compare that to with what is required from you to keep it at that speed. The same physics applies.

9. Batteries- a vast subject. You get what you pay for and their life and degradation of capacity t9 store energy over time depends much on how they are charged over time and depth of discharg and what temperature they operate in and what temperature the heating effect of the current which flows in them causes. Too much to cover right now. I specified top end victron brand batteries. Two years on the first few vans are still performing well on their original batteries.
 
Last edited:
4. I repeat, in order for him to obtain a licence to operate and liability insurance The fridges and freezers have to have power available constantly for them to run as demanded by their thermostats. He previously operated using gennies running during the day and reliant upon the freezer or fridge insulation keeping contents cold enough when the van was closed for business. Alas, another licence holder, using the same scheme sold some burgers which had been defrosted while the gennie was shut down overnight in hot summer period and then refrozen when the genie was running again next day, and then cooked. the punter who ate them was very poorly afterwards.
You are only supposed to freeze raw meet once you see



6. My client buys domestic fridges and they are changed for new every couple of years. He buys LEC and the ones capable of being placed in a warm environment - fridges and freezers have environmental classes to suit where they are used in the world. This should be taken into account also for one placed in a warm garage or conservatory.
Domestic fridges are availbe and as cheep as chips second hand on ebay. And this is why I first considered using them as kegorators as they would do bough the work of the cellar cooler and the beer chiller. But I was concerned about over all power that they would use being to much.

So being an electrion man and since you have worked with domestic fridges. Can I ask you what the typical draw of an typical domestic under the counter fridge would use. And by that I dont mean warm start where it has to chill the contence of the fridge. I just mean its typical power consumtion keeping it all ready cool!



8. Yes, Fs and Fs need time and energy to cool their contents to the point that they are thermostatically regulated in temperature. Opening the door or lid of course will demand some energy during normal operation and placing products inside which need cooling. Every time the motor starts to run the compressor there is a brief surge in power/current drawn to quickly accelerate the mechanical components to running speed. When running the power/current is that necessary to run the refrigeration. Think about you having to quickly run up to speed a children’s roundabout and the compare that to with what is required from you to keep it at that speed. The same physics applies.
Yes I know what you mean! I pedal my bike up to speed then to keep it up to speed is nothing compared to getting it there. But if I let go I free fall all that energy I used to get it up to speed. So in the same way it takes a lot of energy and time to get the fridges to cool the contence. If you switch them off it will take a long time to heat back up again
Thanks
 
9. Batteries- a vast subject. You get what you pay for and their life and degradation of capacity t9 store energy over time depends much on how they are charged over time and depth of discharg and what temperature they operate in and what temperature the heating effect of the current which flows in them causes. Too much to cover right now. I specified top end victron brand batteries. Two years on the first few vans are still performing well on their original batteries.
Ow I hope you dont mind me bringing this question up; but briefly; what make those batteries you buy better then the typical Leisure batteries for caravan found at places like this

Is it the life span or power out put?
Thanks

PS is it some kind of fleet of tea wagons your client runs or something?
 
Fridge or freezer energy consumption: I would look up the specification of the appliance or a number of similar ones and then take the average. So for a typical fridge and freezer whose data sheets are attached the figures are 128kWh per annum and a freezer 209kWh per annum. Divide by 365 to obtain daily consumption. Then consider the difference between the domestic setting these figures refer to and your intended one eg: will the door or lid be opened more or less often.

Thus a larder fridge with auto defrost is 128/365 = 0.35kWh a day (I would assume a figure of 0.5kWh for clients use.)
For chest freezer 209/365 = 0.57kWh (I would assume a figure of 0.7kWh)

Batteries: I am not a battery expect so had to do some research on brands and specifications. I looked at Leisure and Boating forums and googled 'which is the best leisure battery?' or 'is victron a good make of lesiure battery?' There are other good makes no doubt but I settled on Victron which was also stocked by the equipment supplier we used who happens to be close to my client's offices. If I could not obtain a comprehensive specification on the brand and battery I did not consider them.

Victron Advanced Gel Matrix are good because they are safe (don't spill acid), well made, sealed, fully specified and certified, have high charge/discharge cycles, age slowly and provided charged up carefully and discharged to no more than 50% will only slowly fall in storage capacity. Victron is a Dutch company which appealed to my client and me. You will often find Victron equipment in smart motor yachts. We discounted Li ion as too expensive.

Yes teas, coffees, sandwiches, griddle cooked food, chilled soft drinks.

Sir.....spend some time writing down a requirement (what you want and don't want) and then contact a few local off grid supplier for a proposal and price. Or 'do it yourself' noting my earlier remarks well though and you may or may not be successful. My solution had to work and be safe and reliable because it was essential to the bottom line of my client. Your requirement is much different - 2 days a week for how many weeks? One off. You are the operator.......
 
Last edited:

Reply to Advice on buying generator please in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock