Search the forum,

Discuss amp/ wire size noob ? in the UK Electrical Forum area at ElectriciansForums.net

-Hube-

DIY
Reaction score
0
when wiring a 240v 50 amp breaker, for example, does each hot wire have to be rated for 50 amps or 25 amps per wire? 100 amp breaker, 50 amps per wire or 100 per wire. I think I know the answer but not sure. thx.
 
Dang. So my RV box with a 50, 30 and 20 amp receptacle should be wired with #2 wire according to the charts... Also, I had some #8 I was going to use for a 50 amp circuit, but looks like I need to beef it up. Thanks for the reply!
 
#2 or#8 means nothing to us in the UK. We specify wires by the cross sectional area of the conductor, measured in square millimetres. For 50A it would be 10 or16mm2, depending on how it was installed.
 
Interesting... Looks like #2 would be 35mm2. We have a 15' lenth of 8/3 (10mm2) feeding a 240v 50 amp rv recepracle box. It seems like the wire may be too small, or is it ok?
 
A 10mm2 twin and earth cable (which I think is known as 'Romex' in the US) is rated at 63A if fixed, unenclosed , on a wall. This drops to 52A if enclosed in conduit or trunking on a wall, and down to 43A if the conduit is enclosed in a thermally insulating wall.
These are the 'base' figures. They can be reduced further by things like bunching cables together.
 
Yes, Romex is the brand name of the wire here. Looks like the 8/3 is fine then for that 50a outlet. It's unenclosed in an air conditioned room with only about 2' of it outside. Thanks for the info!
 

Reply to amp/ wire size noob ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
873
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
I will describe my problem in as much detail so you guys might be able to answer my question. I am never home, my Electric bill is $ 28 to $30 a...
Replies
23
Views
1K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
1
Views
712
New member and DIY. I have a 60 AMP breaker going to a sub panel for a workshop. Two months ago I bought an electric car and a 40 AMP charger...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock