Discuss Plugging 20 amp a/c into 50 amp outlet in the UK Electrical Forum area at ElectriciansForums.net

Jr70895

DIY
Reaction score
0
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home plugs into a 50 amp outlet to the breaker box inside the trailer.

The central a/c unit was an add on that was installed before I bought the trailer. It has a separate power supply cable that runs from the pedestal and wired directly into the a/c central unit. The cable also plugs into a 50 amp outlet on the pedestal.

The central unit went out and adding a 220 volt 20 amp window unit for now. Need to run 220 wire and install outlet below the window as currently don't have an outlet there.

Hired electrician who's ran 10/2 wire in conduit from the 50amp outdoor pedestal to a new 20amp breaker box attached to the side of the trailer. He will then pigtail inside to new wall outlet.

Several people have since told me that you can't use 10/2 wire and plug it into the 50 amp outdoor pedestal power supply to the breaker box then into the trailer. I'm not an electrician that's why I hired someone.

Was told it should be 6/2 wire from the outdoor pedestal to 20 amp breaker box then pigtail to indoor outlet with 10/2 wire. Right now the 10/2 wire and conduit has been installed but not connected to new breaker box etc. He will be back one day next week to complete.
I'm confused......
I did see online they sell a 50amp to 20amp adapter that could be used to convert 50 amp outlet to 20 amp a/c 220 volt plug.
 

Attachments

  • 61hkJTNVTHL._AC_SX679_.jpg
    37.2 KB · Views: 2
  • 61tfemG3DIL._AC_SL1500_.jpg
    103.2 KB · Views: 3

I guess no one can answer my question....Thanks
Thank you for the picture.
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home plugs into a 50 amp outlet to the breaker box inside the trailer.

The central a/c unit was an add on that was installed before I bought the trailer. It has a separate power supply cable that runs from the pedestal and wired directly into the a/c central unit. The cable also plugs into a 50 amp outlet on the pedestal.

The central unit went out and adding a 220 volt 20 amp window unit for now. Need to run 220 wire and install outlet below the window as currently don't have an outlet there.

Hired electrician who's ran 10/2 wire in conduit from the 50amp outdoor pedestal to a new 20amp breaker box attached to the side of the trailer. He will then pigtail inside to new wall outlet.

Several people have since told me that you can't use 10/2 wire and plug it into the 50 amp outdoor pedestal power supply to the breaker box then into the trailer. I'm not an electrician that's why I hired someone.

Was told it should be 6/2 wire from the outdoor pedestal to 20 amp breaker box then pigtail to indoor outlet with 10/2 wire. Right now the 10/2 wire and conduit has been installed but not connected to new breaker box etc. He will be back one day next week to complete.
I'm confused......
I did see online they sell a 50amp to 20amp adapter that could be used to convert 50 amp outlet to 20 amp a/c 220 volt plug.
I really don’t see why it wouldn’t work since the electrician installed a sub panel and the AC is protected by a 20 or 30 amp breaker. According to the picture I’m going to assume that the middle receptacle is the one that’s going to be used. If it is used for any other loads then yes it should be #6 wire
 
Thank you for the picture.

I really don’t see why it wouldn’t work since the electrician installed a sub panel and the AC is protected by a 20 or 30 amp breaker. According to the picture I’m going to assume that the middle receptacle is the one that’s going to be used. If it is used for any other loads then yes it should be #6 wire

Yes, the center outlet will be used. This is all part of the original power supply that the trailer plugs into. You can see the main power cable from the pedestal that runs into the trailer that’s plugged in. The old cable is lying on the ground. Will use that outlet and run 10 gauge wires from the 50 amp outlet to the 20 amp breaker then pigtail into the trailer.
Several folks said you can’t do that. That you can’t use the 30 amp rated wire.
50 amp outlet, 30 amp wire being used, ran to a 20 amp outdoor breaker then pigtailed inside to the 20 amp outlet.
Was told wire must be 50 amps to the breaker box.
That’s why I’m so confused. If in fact it’s changed to 50 amp 6/3 wire from the outdoor existing pedestal to the new breaker box can it be wired to a 20 amp breaker box then pigtailed into the trailer?
I’m assuming the electrician has a handle on it and knows what he’s doing.
 
Yes, the center outlet will be used. This is all part of the original power supply that the trailer plugs into. You can see the main power cable from the pedestal that runs into the trailer that’s plugged in. The old cable is lying on the ground. Will use that outlet and run 10 gauge wires from the 50 amp outlet to the 20 amp breaker then pigtail into the trailer.
Several folks said you can’t do that. That you can’t use the 30 amp rated wire.
50 amp outlet, 30 amp wire being used, ran to a 20 amp outdoor breaker then pigtailed inside to the 20 amp outlet.
Was told wire must be 50 amps to the breaker box.
That’s why I’m so confused. If in fact it’s changed to 50 amp 6/3 wire from the outdoor existing pedestal to the new breaker box can it be wired to a 20 amp breaker box then pigtailed into the trailer?
I’m assuming the electrician has a handle on it and knows what he’s doing.
Will it work? Yes. Will the trailer burst into flames? No. But code allows a remote structure (trailer) to be powered with ONE circuit, which could be a 120 volt feeder (like to a detached garage from a house for a couple of lights, outlets, etc...) or a 240/120 volt multi-wire branch circuit like from a house (or pedestal) to a garage sub-panel for multiple 120v/ 240v circuits... but not TWO circuits. As the central a/c condenser previously fed from a separate pedestal circuit was located outside the structure I suppose most inspectors would allow it since the 2nd circuit does not enter the structure. But now you are entering the structure with a second feeder which technically, according to NEC is a violation.
 

Reply to Plugging 20 amp a/c into 50 amp outlet in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Trying to connect a 50 amp inlet box to my Siemens outdoor combination panel 200 amp cutoffs. Can’t figure out where to insert the 50 amp breaker...
Replies
1
Views
848
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
729
Hi, can a 60a AC disconnect fuse box with 2 class K busman 50amp fuse work as a disconnect near the outlet ? Or would it need to be an actual...
Replies
1
Views
413
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
473

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock