Table A.3 Page 105 Guidance note 3:
"Table A.3 gives the multipliers to be applied to the value given in table A.1 for the purpose of calculating the resistance at the maximum operating temperature of the line conductors and /or CPC in order to determine compliance with the earth fault loop impedance of tables 41.2,41.3,41.4 of BS 7671."
The multipliers being 1.2 for 70 C thermoplastic insulation.
So this says to me that if you use the 1.2 multiplier then there is no need to also use the 0.8 multiplier.
You either use one or the other not both.
If you use 0.8 you do not use 1.2
If you use 1.2 there is no need to use 0.8
Any thoughts people?
I have to get this right myself also.
"Table A.3 gives the multipliers to be applied to the value given in table A.1 for the purpose of calculating the resistance at the maximum operating temperature of the line conductors and /or CPC in order to determine compliance with the earth fault loop impedance of tables 41.2,41.3,41.4 of BS 7671."
The multipliers being 1.2 for 70 C thermoplastic insulation.
So this says to me that if you use the 1.2 multiplier then there is no need to also use the 0.8 multiplier.
You either use one or the other not both.
If you use 0.8 you do not use 1.2
If you use 1.2 there is no need to use 0.8
Any thoughts people?
I have to get this right myself also.