Discuss An Awful Feeling This in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

A BS EN 60898 circuit breaker has an lcn of 10 kA and an Ics rating of 6 kA.
State
a) how the circuit breaker is likely to perform if the circuit developed a fault current of 8kA (1 mark)
b) the likely operational condition of the circuit breaker following the fault (1 mark)
c) the action that would need to be taken to ensure the circuit was protected should a similar fault occur in the future. (1 mark)

This is one topic i have not covered in depth, correct me if i am wrong here

Uo/Zs = Ia
 
A BS EN 60898 circuit breaker has an lcn of 10 kA and an Ics rating of 6 kA.
State
a) how the circuit breaker is likely to perform if the circuit developed a fault current of 8kA (1 mark)
b) the likely operational condition of the circuit breaker following the fault (1 mark)
c) the action that would need to be taken to ensure the circuit was protected should a similar fault occur in the future. (1 mark)

This is one topic i have not covered in depth, correct me if i am wrong here

Uo/Zs = Ia

Ics is the max fault value that a device can clear and be put back into service again.

Icn is the max fault value that a device can clear but the device will not function again.

A) The device will interrupt the fault.

B) The device will not be operational.

C) The protective device should be replaced.
 
Ics is the max fault value that a device can clear and be put back into service again.

Icn is the max fault value that a device can clear but the device will not function again.

A) The device will interrupt the fault.

B) The device will not be operational.

C) The protective device should be replaced.

i have just paid for a copy of the regs online so i will have a bit of reference material, so the circuit breaker would be faulty, thanks

i have been looking in gn3 for information on 100mA rcds, i know they are tested at times half and at times 1 but i cant find any info on tripping times, if i remember correctly its 200 ms for the bs one and is it 300 ms for 61009
 
Just remember BS EN RCD have 300ms trip time

BS numbered RCD is 200 ms..

Remember the EN as extra time to trip.

You only do the 5x test on 30mA RCD

thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky
 
Last edited by a moderator:
Value of resistivity for 1.5mm = 12.10 milliohms per metre
Value of resistivity for 10mm = 1.83 milliohms per metre

Therefore (R1&R2) resistivity in milliohms per metre = 12.10+1.83 = 13.93 milliohms per metre
Length = 28m
Factors = 1.02 & 1.20 (from tables 9B and 9C OSG)

Therefore, R1&R2 = (milliohms per metre x Length x Factor) / 1000

= (13.93 x 28 x 1.02 x 1.20) / 1000 = 0.48 ohms.

Zs = Ze + (R1&R2)

= 0.14 + 0.48 = 0.62 ohms

I have been thinking about this.
Value of resistivity for 1.5mm = 12.10 milliohms per metre
Value of resistivity for 10mm = 1.83 milliohms per metre

Therefore (R1&R2) resistivity in milliohms per metre = 12.10+1.83 = 13.93 milliohms per metre
Length = 28m

I agree, these figures are taken from table A.1 and are the value at 20C
Therefore at 20C our circuit resistance would be
13.93*28/1000 = 0.39 Ohms.

We have designed the circuit at 25C so if we were to measure the R1+R2 value at 25C we would need to add a correction factor because at 25C the resistance would be slightly higher, this correction factor is 1.02.
So the realistic resistance figure at 25C for our circuit would be:
.39 Ohms * 1.02 = 0.398 Ohms

This is what the correction factors for ambient temperature are for, they are to be applied to the tables EG table A.1 to change the values in those tables measured at 20C to whatever temperature the circuit is being measured at in reality.

Now The rule of thumb (the .8 rule) is used to multiply the tabulated figures in BS7671 which are measured at 70C
The 0.8 is used to bring the figures measured at 70C down to a figure that they would be if the circuit were measured at 20C.
Conversely if we want to convert our figure of R1+R2 measured at 20C to a figure measured at 70C we would multiply it by 1.2 this figure would then become our R1 + R2 measured at 70C and we would add Ze to this. We would then be able to compare this figure directly to the tables in BS 7671.

So in this instance we need the figure for the circuit we are designing, the R1 + R2
measured at 20C.
We calculate what this figure is by using the above formula EG:
13.93*28/1000 = 0.39 Ohms.
This is the figure at 20C.
We then multiply the figure at 20C by a factor of 1.2.
0.39 * 1.2 = 0.468 Ohms.
Add this to Ze
Zs = .14 + .468 = 0.608 Ohms.
This is the figure we would use to compare to figures in BS 7671.
We would not use the ambient temperature figure in this calculation.
The only time we would use the ambient temperature correction factor of 1.02 was if we were measuring our R1+R2 at 25C and we needed to compare these measured figures with those in the book which were recorded at 20C
We would take the figures in the book measured at 20C multiply them by a factor of 1.02 and this would give the value of the table figures at 25C.
We would then be able to compare our measured reading at 25C directly to these tabulated figures.
We would not use both the factors of 1.02 and 1.2 together in the same calculation.

This is how it appears to me, shoot me down if I am wrong.

One more thing, I noticed a nice little fact today.
The resistance of copper will increase by 2% for every 5C increase in temperature.
So if in doubt use this way to measure what the resistances would be at different temperatures.
If a cable increases in temperature from 20C to 70C its resistance will increase by 20%
 
Last edited:
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

B is also 5% I think, it's not a lighting circuit so it is 5%

I do not know the reason for the difference in the 3% and the 5% I just know it's a fact set in stone so I don't argue with it.
 
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

It's 8% from a private supply source.

The reason for the lower level for lighting is that some types of lighting cannot strike up on lower voltages so tolerances are tighter.
 
Last edited:
Hi

for single phase 3% for lighting 6.9v
5% for power circuits and distribution 11.5v
and for the answer to b) its 20V which is 5% of 400v

no sorry i am wrong its not 20V as its there own supply not sure
 
thanks

Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

Have a look at Appendix 12 in BS 7671 it covers VD only.
 
Hi

for single phase 3% for lighting 6.9v
5% for power circuits and distribution 11.5v
and for the answer to b) its 20V which is 5% of 400v

no sorry i am wrong its not 20V as its there own supply not sure

I'm guessing it's 5% per phase so it's 11.5V at each phase where the equipment is installed, not measured between phases.
But I'm guessing.
Sorry it's 8% from a private supply source (This is a new one for me) so I am guessing it is 8% per phase = 18.4 V
But it's just a guess so hopefully I'll be put right by someone.
 
Last edited:
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

Spot on, the percentage is actually of 400 Volts ie. 32 Volts
 
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze + (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?
 
Last edited by a moderator:
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze = (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?

I can't confirm the mOhm values but the maths is correct.

You MUST use (R1+R2) when doing these calculations and remember that r1, rn and r2 are reserved for ring continuity figures, this exam is very big on correct terminology.
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

just ordered a set of regs from fleabay so they should be with me in the next couple of days - the only problem i found with the regs in the past was navigating them, i always favoured the on site guide for obvious reasons
 
New posts

Reply to An Awful Feeling This in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
846
Hi everyone, Sorry, I won't take much of your time. To cut a long story short, I am newly qualified and have domestic installation/commercial...
Replies
0
Views
431
Hello! I am looking for a company to allow me to get more electrical experience. I am mid 30’s, ex military officer and currently training on the...
Replies
2
Views
1K
Hi everyone, I’ve been a long time viewer of the forums and have used many times to answer queries I have come across. I am a 26 year veteran...
Replies
4
Views
301
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock